Hello all,

I am wondering if there is setpoint manager similar to the SetpointManager:OutdoorAirReset that can be used to vary a water temperature based on the outdoor air temperature?

Thanks

Dustin's avatar
1.1k
Dustin
asked 2016-02-04 10:12:44 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-02-04 10:38:14 -0500
edit flag offensive 0 remove flag reopen merge delete

Closed for the following reason "the question is answered, right answer was accepted" by Dustin 2016-02-04 10:44:45 -0500

Comments

add a comment see more comments

1 Answer

2

How about SetpointManager:OutdoorAirReset :) ?

It works on plant loop just fine too. The documentation is pretty confusing on this since it mentions Supply Air temperature, but a plant loop will gladly accept it too. In fact, for many of the water reset (Hot water or chilled water) in ASHRAE Appendix G, this is what you need to use.

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2016-02-04 10:25:24 -0500, updated 2016-02-04 10:28:07 -0500
edit flag offensive 0 remove flag delete link

Comments

I've found the related question I was thinking about: here

Julien Marrec's avatar Julien Marrec (2016-02-04 10:29:24 -0500) edit

Thanks Julien that was confusing me where it said Supply Air temperature. I appreciate the quick response.

Dustin's avatar Dustin (2016-02-04 10:44:40 -0500) edit
add a comment see more comments