2

What is the Cooling Sizing Parameters - Zone Cooling DesignSupply Air Temperature for?

What is the Cooling Sizing Parameters - Zone Cooling DesignSupply Air Temperature for?

VictoriaEagen's avatar
556
VictoriaEagen
asked 2016-02-03 20:20:30 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-02-03 23:06:29 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

That parameter is used in the zone sizing calculation to determine the volume of air required to cool the zone to the zone thermostat setpoint temperature at design conditions. If you use any sort of auto-sizing capability in your simulation, this is a very good chapter of the documentation to familiarize yourself with.

ericringold's avatar
10.6k
ericringold
answered 2016-02-03 21:00:30 -0500
edit flag offensive 0 remove flag delete link

Comments

So it is kind of like what you would want the air temperature to be supplied at to over compensate for the load? Is this a calculation I need to do?

VictoriaEagen's avatar VictoriaEagen (2016-02-03 23:16:27 -0500) edit
add a comment see more comments