Is there an "unmet hours" output variable equivalent for DHW demand?

If we want to see if our heating/cooling system is adequately-sized we can use the Facility Heating Setpoint Not Met While Occupied Time (i.e. unmet hours) output variable. Is there anything similar which can tell us if our domestic hot water demand is not being met?

Alternatively (since I can't see anything obvious), what would be a simple calculation from outputs which are available?

Jamie Bull's avatar
5.1k
Jamie Bull
asked 2016-01-27 04:37:49 -0500
MatthewSteen's avatar
10.1k
MatthewSteen
updated 2016-01-27 08:01:19 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

5

I cannot think of a time-based output, but the output variable called "Water Use Connections Hot Water Temperature" should be compared to the intended hot water supply temperature setpoint.

Archmage's avatar
7.2k
Archmage
answered 2016-01-27 06:23:39 -0500
edit flag offensive 0 remove flag delete link

Comments

I thought that might be the answer. I was actually about to post it myself, hence the slight change to the question. Beat me to it!

Jamie Bull's avatar Jamie Bull (2016-01-27 06:26:20 -0500) edit
add a comment see more comments
3

If your WaterUse:Connections is the only thing on the demand side of your plant loop, or you can safely assume the rest is satisfied, then you can use the Plant Loop Unmet demand rates:

HVAC,Average,Plant Supply Side Unmet Demand Rate [W]
HVAC,Average,Plant Supply Side Not Distributed Demand Rate [W]

See documentation here