What are the Energy Efficiency Rates for ASHRAE baseline refrigeration equipment

I am modeling a milk processing plant and need to know the EERs for the ASHRAE baseline cooling equipment.

bednarek1's avatar
21
bednarek1
asked 2016-01-25 09:28:07 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-01-25 12:46:29 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

0

For refrigeration equipment, you should enter the same performance for your baseline as what you are using in the proposed model. There is no explicit way of getting credit for high performance refrigeration equipment in Appendix G (Standard 90.1-2004 thru 90.1-2013).

For some organizations that reference Appendix G, you may be able to make a special request to get credit for refrigeration equipment is higher performance than what is typically installed in buildings. That would be up to the individual organization.

JasonGlazer's avatar
6.8k
JasonGlazer
answered 2016-02-03 16:32:00 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

ASHRAE 90.1 deal directly with applications related to occupant comfort. Because the refrigeration system in a refrigerated warehouse is not trying to achieve occupant comfort, 90.1 considers it more of a process load. However, there has been some work done to develop a baseline for refrigerated warehouses by IACSC-IARW. It looks like from this link that GBCI has approved it for LEED as well.