Plant Operation Schemes in EnergyPlus example files

Several EnergyPlus example files (e.g. CoolingTower.idf, ElectricEIRChiller.idf, CentralChillerHeaterSystem_Cooling_Heating.idf etc. to name a few) have two cooling load range based plant operation schemes specified for on peak and off peak operation. But same operation scheme name ("Peak Operation") was specified for both on peak and off peak periods. Some of these files which do have "Off Peak Operation" cooling load based operations scheme, they refer to same plant equipment list which is associated with "Peak Operation" scheme. This seems counter intuitive as this means that same plant equipment is always running to meet the cooling loads regardless of peak/off peak period and that second cooling load based scheme is actually redundant.. Is this as designed? Another question on UnmetHours led to this current question.

Chandan Sharma's avatar
2.4k
Chandan Sharma
asked 2015-12-23 18:43:52 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

This is a known issue that has propagated across many example files. For each one, it should be fixed to use an appropriate equipment list, or the dual schedules should be removed. https://github.com/NREL/EnergyPlus/is...

MJWitte's avatar
9.7k
MJWitte
answered 2016-01-12 10:39:50 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you Mike.