Chiller Heat recovery Net metering

I am setting up a heat recovery chiller and want to connect the recovered heat to a campus hot water loop. Is this arrangement possible. Or is there a work around that I could use to determine the total heat rejected by the heat recovery chiller.

kbk78's avatar
601
kbk78
asked 2015-12-16 20:08:45 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2015-12-17 09:17:03 -0500
edit flag offensive 0 remove flag close merge delete

Comments

On similar count it is possible to have a chiller heater follow the heating load and transfer the excess chilled water to the campus chilled water loop.

kbk78's avatar kbk78 (2015-12-17 09:58:31 -0500) edit
add a comment see more comments

2 Answers

2

Someone has asked a similar question HERE. You would need to connect chiller heat recovery stream to storage tank, then have the storage tank serve as HW supply to campus hot water loop. You will likely need to use a Fluid to Fluid HX object to have the chiller heat recovery water provide heat to the campus hot water loop. Reference the schematic below.

image description

Aaron Boranian's avatar
14.1k
Aaron Boranian
answered 2015-12-17 09:30:14 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
1

Yes, this arrangement is possible. Please take a look at HeatRecoveryElectricChiller.idf example file.