Problem with HVAC Systems (Sizing Zone) in OpenStudio.

Hello,

I have problem with HVAC Systems in OpenStudio. In my model i created simple loop of water and air system but i can't make correctly simulation. I have errors like in the picture - "Sizing Zone". I tried to change software properties (simulation control), but it doesn't help. Thermal Zones, all properties of system element are OK (I think).

This system is only example. I didn't put there real values and elements. After correct simulation of this simple loop i will edit it according to my project. image description image description image description

buaszej's avatar
41
buaszej
asked 2015-12-07 08:48:10 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-05-08 15:46:32 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

5

You're missing an air terminal unit on your air loop to supply to the zone. (Example: Air Terminal Single Duct Uncontrolled)

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2015-12-07 09:12:09 -0500
edit flag offensive 0 remove flag delete link

Comments

It's working now, thanks.