How to modifying design day conditions as per ASHRAE 90.1 G1.2.2.1?

Is there a way to override the OpenStudio 1.9 site tab design day conditions to 1% cooling design temperatures and 99.6% heating design temperatures as required by ASHRAE 90.1 G3.1.2.2.1 without having to manually look up these values in the weather file and entering them into multiple places? image description

Could future versions of OpenStudio have a function similar to Trace (see screenshot) where you select a button for the design day you would like when importing from the ddy file? All of the information is already in the ddy file 0.4%, 1.0%, and 2.0%, it just defaults to 0.4% cooling design with no option for anything else. image description

kramerica's avatar
1.1k
kramerica
asked 2015-11-30 18:25:57 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-01-20 13:40:26 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

You could write a simple Measure to do this, but there currently isn't a way to do this in the GUI apart from manually typing it in. However, this is a good feature request, so I've added it to the list. If you like this idea, go here to upvote it.

aparker's avatar
8.2k
aparker
answered 2015-12-01 19:19:20 -0500
edit flag offensive 0 remove flag delete link

Comments