Variable Speed Fan (AHU)

I developed a model with Packaged Terminal Heat Pump Air Loop with a Variable Speed Fan (Air Handler Unit). However, the model gives constant hourly fan energy values and this does not match the actual data. How do I get the fan energy to vary. image description

Attached is the hourly energy consumption of the measure and simulated model.

image description

Update:

Here is the link to the OpenStudio Model

tajjmann's avatar
455
tajjmann
asked 2015-11-25 12:58:01 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2015-12-01 07:16:17 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Are you sure that you are looking at the output variable from the correct fan? I noticed that you have a second fan on the OA intake.

aparker's avatar aparker (2015-11-25 15:56:08 -0500) edit

(Side note: shouldn't the fan on the OA be turned upside down graphically?)

Julien Marrec's avatar Julien Marrec (2015-11-26 02:55:56 -0500) edit

@aparker the other fan on the OA intake is an ERV system and am very sure of the output variable @Julien Marrec

tajjmann's avatar tajjmann (2015-11-26 12:59:11 -0500) edit

@tajjmann: this is not what I meant. I just meant that graphically openstudio should probably display the fan differently, i.e. flipped so that, like your supply fan, the blade is after the box. This doesn't affect what's really being modeled by EnergyPlus

Julien Marrec's avatar Julien Marrec (2015-11-27 02:50:51 -0500) edit

As far as troubleshooting, it would help to have your openstudio model itself if you can share it.

Julien Marrec's avatar Julien Marrec (2015-11-27 02:52:10 -0500) edit
add a comment see more comments