Consumption report

I'm doing a new building, and only to check if I get errors in my geometry I simulate the model. I use the loads and constructions by default.

I check the OpenStudio results summary and I get no values, this is normal?

Thanks

image description image description

J Monteiro's avatar
1.2k
J Monteiro
asked 2015-10-06 11:36:16 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-01-27 18:48:29 -0500
edit flag offensive 0 remove flag close merge delete

Comments

No this is not normal. Looks like the measure to show results is not working. What version of OpenStudio are you using, looks like 1.8.0 or earlier. If you go to the EnergyPlus do yo see results there? Did you by any chance add in a measure to change the tabular results to IP units? That would cause this error, but there could be other causes.

David Goldwasser's avatar David Goldwasser (2015-10-06 23:12:31 -0500) edit

I'm using OpenStudio 1.8.0 with Windows 7 32 bit. I don't add any measure. I edit my question and has you can see the EnergyPlus gives me a building area of 0 m2.

This project was started by my colleague with OpenStudio 1.8.0 and Windows 8.1 64 bit.

J Monteiro's avatar J Monteiro (2015-10-07 03:10:48 -0500) edit

I figure now that I don't have a Building Component Library (BCL) Account, this could be the problem?

J Monteiro's avatar J Monteiro (2015-10-07 04:13:49 -0500) edit

BCL account doesn't have anything to do with this.

aparker's avatar aparker (2015-10-07 09:09:06 -0500) edit
add a comment see more comments

1 Answer

2

Building area of 0 is a clue, looks like you don't have any of the spaces in your model associated with thermal zones. You can associate spaces with thermal zones either using the Plugin, or with the "Spaces" tab in the OpenStudio application 1.9 (or facility tab in 1.8 or earlier).

David Goldwasser's avatar
20.4k
David Goldwasser
answered 2015-10-07 09:27:48 -0500
edit flag offensive 0 remove flag delete link

Comments

I found the problem. It's like you said, I forgot to assign thermal zones.

J Monteiro's avatar J Monteiro (2015-10-08 03:07:10 -0500) edit