SimHVAC and convergence issue

I am modeling an office building seved by VAV systems. I am getting a huge amount of SimHVAC convergence issue. After investigating, it looks like these errors might be coming from the fact that I am using a SetpointManager:WarmestTemperatureFlow to control the supply air temperature, as when I switch to a Scheduled or OutdoorAirReset setpoint manager I don't have these issues. Also, it looks like my model fit case 3 from this article.

Is it possible to avoid these non-convergence issues?

Jeremy's avatar
1.6k
Jeremy
asked 2015-09-22 12:03:59 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Using the example file 5ZoneCAV_MaxTemp and running an annual simulation with no other changes to the file also causes max iteration warnings, although these were from SolveAirLoopControllers. We are beginning to look into these issues and I will add this file to the list of problem files. I suggest you add your file as well so we correct as many of these issues as possible.

rraustad's avatar
13.8k
rraustad
answered 2016-04-06 18:58:31 -0500
edit flag offensive 0 remove flag delete link

Comments

@rraustad I am going to try to dig it up!