DX-Coil for data center applications

I'm using energyplus to simulate a data center. CRAC units with correspondingly high capacities often have 2 stages. So I 'm using the coil object Coil:Cooling:DX:TwoStageWithHumidityControlMode.

Is it necessary to set the "Enhanced Dehumidification Mode" to 1 for the control types "CoolReheat" and "Multimode"? Or are both of these parameters independent of each other?

Furthermore I'm not sure which control type is the right one for typical CRAC units?

nielex's avatar
139
nielex
asked 2015-09-19 08:33:54 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2015-09-20 07:54:21 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Per the documentation (scroll down to field "Number of Enhanced Dehumidification Modes"), yes this field should be set to 1 for enhanced dehumidification control types. In E+ v 8.3, example file 1ZoneDataCenterCRAC_wPumpedDXCoolingCoil.idf models data center with CRAC units which could be a good starting point here.