How to include ventilation in residential spaces in CBECC-Com?

I have a high rise residential building where the dwelling units do not include cooking (it is a senior retirement facility). I have modeled the dwelling units as High-Rise Residential Living Spaces function, which has an occupancy class of Residential.

This removes the option of adding ventilation at the HVAC zone yet I got a review comment from the code official indicating that I need revise the Title 24 form Part N to include the outside air requirements for these systems. Note that these systems include outside air in the mechanical design.

Any suggestions on what I should do? Do I need to change the occupancy class to non-residential?

anchapin's avatar
626
anchapin
asked 2015-09-01 10:42:50 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-11-07 14:31:19 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

CBECC-Com does not currently model ventilation systems for residential spaces and models them using two 'ZoneInfiltration:DesignFlowRate' objects on each zone to account for it. It obviously means that fan power and any conditioning by an additional system is not accounted for all that accurately. There is a discussion here and here that highlight some of the issues. You could perhaps pass along the second link to the plan checker where it says "Residential System are to be definited with no explicit outside air ventilation"