EnergyPlus IdealLoadAirSystem vs. Internal Gains

I run a simulation with HVAC:Template:IdealLoadAirSystem with a constant heating setpoint 20°C (in January, max outside temperature 13°C). Then i calculatet - from the Zone Ideal Loads Zone Total Heating Energy the - the required Energy in Watt. Imported that file through schedule:File and add "ElectricEquipment" with schedule Name (the name from schedule:file) + delete the IdealLoadAirSystem.

The result I expacted: The zone air temperature is 20°C The result I get: The Electric Equipment Total Heating Energy is the same than the Ideal Zone Total Heating Energy. But the temperature i different (up to 2K). Has anybody an idea?

gerald's avatar
523
gerald
asked 2015-08-26 09:56:58 -0500
MatthewSteen's avatar
10.1k
MatthewSteen
updated 2015-08-29 18:02:57 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

I would guess the ElectricEquipment has a radiative fraction so not all its heat is hitting the zone air. The part that hits surfaces as infrared radiation can conduct out the surfaces.

Archmage's avatar
7.2k
Archmage
answered 2015-08-26 10:41:42 -0500