OpenStudio System Sizing Settings

I was modeling a simple air loop in OpenStudio, in the exported EnergyPlus IDF file, the "Sizing:System" object shows that the "100% Outdoor Air in Cooling" and the "100% Outdoor Air in Heating" were automatically set to "Yes". I think this would lead to significant over sizing of the cooling and heating coils. However, I did not find a place in the OpenSutdio user interface that I can specify these two fields to "No".

image description

image description

TiejunWu's avatar
563
TiejunWu
asked 2015-08-11 11:10:39 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-08-11 11:30:44 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

7

Clicking the dotted line separating the Supply and Demand sides of the air loop exposes the drop-down fields to change these inputs in the Edit pane:

image description

ericringold's avatar
10.6k
ericringold
answered 2015-08-11 11:36:26 -0500
edit flag offensive 0 remove flag delete link

Comments

Yes the fact that we are oversizing because of this setting has not gone unnoticed. Is it time to reconsider this default?

Kyle Benne's avatar Kyle Benne (2015-08-11 16:32:31 -0500) edit

@Kyle Benne - Interesting question IMO; this simple control (ON/OFF) is helpful for systems that use a large % of OA (gyms, auditoriums, etc.) as well as for identifying an upper-limit on potential equipment size. That being said, having it default to ON may not be the best if that majority of users either don't require/understand this control setting.

NickC's avatar NickC (2015-08-17 15:33:00 -0500) edit