Modeling electric resistance heater in CBECC

I am trying to model electric unit heater for a stairwell in CBECC Non-Res 2022 but for some reason when I use 'furnace' as my zone system and create a heating coil(electric resistance) with a fan, the output report spits out that there is a no cooling system for that stairwell and assigns it a random cooling coil capacity. It seems that the software is thinking that there should be a cooling happening although there is none. I have tried unchecking the box where it says 'add cooling system to meet the load' but no luck. Please guide if you have any idea.

Abdul1236's avatar
11
Abdul1236
asked 2024-09-21 18:08:32 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2024-09-22 11:54:45 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

In general, all conditioned spaces are evaluated in both heating and cooling for compliance purposes. So yes, your stairwell will have a dummy cooling system added to it even though there's nothing installed in reality. I don't have this part of the ACM memorized, but it's going to be an autosized cooling system matching the Standard Design system type and ratings.

LukeInCali's avatar
86
LukeInCali
answered 2024-09-23 10:03:31 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks for the insights. I see. So it’s fine to leave it as auto sized as is right now? I was wondering if I needed to get rid of it but seems I cant. It’s not bothering in terms of overall compliance results or UMLH.