Yes, you can do it in the OpenStudio Application.
- Put a chiller onto the supply side of the Chilled water loop, and then on the demand side (via the My Model tab!) of the condenser loop.
- Now go to your heat recovery loop, and drag again the same chiller from "My Model" tab to the demand side of that loop. Your chiller will be on all three loops.
- The OpenStudio SDK logic in
addToNodeis that if you try to connect aChillerElectricEIRto the demand side of a loop, if it's already connected on the demand side and does not have a Heat Recovery yet, thenaddToTertiaryNodeis called. (see C++ source here)
addToTertiaryNode is still perfectly valid.
ChillerElectricEIRis aWaterToWaterComponent, and the method is there (and functional, I just tested). https://s3.amazonaws.com/openstudio-sdk-documentation/cpp/OpenStudio-3.7.0-doc/model/html/classopenstudio_1_1model_1_1_water_to_water_component.html- Your mistake is very likely that you aren't working with the chiller as a
ChillerElectricEIRor aWaterToWaterComponentbut probably as an HVACComponent or a ModelObject. You need to cast it, viamodelObject.to_ChillerElectricEIR.get
- The
OpenStudio SDKlogic inaddToNodeis that if you try to connect aChillerElectricEIRto the demand side of a loop, if it's already connected on the demand side and does not have a Heat Recovery yet, thenaddToTertiaryNodeis called. (see C++ source here)