Surprisingly, EnergyPlus still lacks a feature of variable condenser water flow as of V23-2-0. I referred to @Julien Marrec and @Gio 's 4 year old answers.
My case is as follows. The condenser water loop has 6 nos. of CoolingTower:SingleSpeed and one HeaderedPumps:VariableSpeed with 6 pumps in bank.
After much consideration, my EMS was finally as follows.
SetpointManager:FollowOutdoorAirTemperature,
CHWloop CndW Temp Manager, !- Name
Temperature, !- Control Variable
OutdoorAirWetBulb, !- Reference Temperature Type
3.6, !- Offset Temperature Difference {deltaC}
32, !- Maximum Setpoint Temperature {C}
5, !- Minimum Setpoint Temperature {C}
CHWloop CndW Supply Setpoint Nodes; !- Setpoint Node or NodeList Name
ChW_Supply_Cooling_Demand, !- Name
CHWloop Chilled Water Loop, !- Output:Variable or Output:Meter Index Key Name
Plant Supply Side Cooling Demand Rate; !- Output:Variable or Output:Meter Name
CndW_Supply_Inlet_Temp, !- Name
CHWloop Condenser Water Loop, !- Output:Variable or Output:Meter Index Key Name
Plant Supply Side Inlet Temperature ; !- Output:Variable or Output:Meter Name
Site_OA_WB, !- Name
Environment, !- Output:Variable or Output:Meter Index Key Name
Site Outdoor Air Wetbulb Temperature ; !- Output:Variable or Output:Meter Name
CndW_Demand_Outlet_Temp, !- Name
CHWloop CndW Demand Outlet, !- Output:Variable or Output:Meter Index Key Name
System Node Temperaure ; !- Output:Variable or Output:Meter Name
EnergyManagementSystem:Actuator,
CndW_Supply_Pump_Mass_Flow, !- Name
CndW Supply Pump,!- Actuated Component Unique Name
Pump, !- Actuated Component Type
Pump Mass Flow Rate; !- Actuated Component Control Type
EMS_PCM_CndW_Supply_Pump_Mass_Flow_Override, !- Name
InsideHVACSystemIterationLoop, !- EnergyPlus Model Calling Point
EMS_Program_CndW_Supply_Pump_Mass_Flow_Override; !- Program Name 1
EMS_Program_CndW_Supply_Pump_Mass_Flow_Override, !- Name
IF ChW_Supply_Cooling_Demand == 0, !- Program Line 1
SET CndW_Supply_Pump_Mass_Flow = 0, !- Program Line 2
ELSEIF CndW_Supply_Inlet_Temp <= 5, !- A4
SET CndW_Supply_Pump_Mass_Flow = 80.3, !- A5
ELSEIF CndW_Demand_Outlet_Temp >= 40, !- A6
SET CndW_Supply_Pump_Mass_Flow = 963.8, !- A7
ELSEIF Site_OA_WB <= 1.4, !- A8
SET CndW_Supply_Pump_Mass_Flow = @MIN (@MAX 20.075 (ChW_Supply_Cooling_Demand * 1.25 / 4180 / (CndW_Supply_Inlet_Temp - 5))) 963.8, !- A9
ELSE, !- A10
SET CndW_Supply_Pump_Mass_Flow = @MIN (@MAX 20.075 (ChW_Supply_Cooling_Demand * 1.25 / 4180 / (CndW_Supply_Inlet_Temp - (Site_OA_WB + 3.6)))) 963.8, !- A11
ENDIF; !- A12
The chart below shows the condensor water pump flow rate of two cases (No EMS and With EMS) in May as an example. The building has retails, restaurants and plant rooms, and chillers run 24h/day. Please note that since the condenser water pump is a headered pump with 6 pumps in bank, the condenser water flow rate varies to some extent according to the number of cooling towers in operation even if there is no EMS. HeaderedPumps:VariableSpeed acts as if it is HeaderedPumps:ConstantSpeed if there is no EMS.
The annual electricity end uses are -51.4% condenser water pump, +8.8% heat rejection, +0.3% cooling, and -0.1% chilled water pump in my case. The total end use of above 4 categories is -10.3%. No increase in the cooling unmet hours.
Here are some findings.
I had to use
Plant Supply Side Cooling Demand Rate[W] of Chilled water loop instead of Condenser water loop to calculatePump Mass Flow Rateof the condenser water pump. When I usedPlant Supply Side Cooling Demand Rate[W] of Condenser water loop, it became zero andPump Mass Flow Rateof the condenser water pump became zero as well. The simulation did not terminate, but I got thousands of unmet hours as the cooling load was not handled. I could not identify the cause, but there may be something wrong during warmup. When I usedPlant Supply Side Cooling Demand Rate[W] of Chilled water loop, I multiplied 1.25, which is shown in the lines A9 and A11 ofEnergyManagementSystem:Program. It is becauseOutput:variables showed that Condenser water cooling demand rate is around 25% larger than Chilled water cooling demand rate on average, which is aligned with this discription in I/O Reference.The equation of mass flow rate that Julien showed could not be used as it is. The simulation starts with the minimum water temperature for both inlet and outlet i.e., TEWT = TLWT. The denominator of the equation becomes zero at the start of the simulation. I got the following severe error and the simulation terminated. I wanted to avoid the severe error above, but I needed to drive the condenser water pump at the start of the simulation. So, I have set the constant condenser water pump flow rate (80.3kg/s which is equal to the smallest pump of 6 pumps in bank) when the condenser water loop supply inlet temperature is 5ºC which is the
Minimum Loop TemperatureofCondenserLoopin my case. The code is shown in the line A4 and A5 ofEnergyManagementSystem:Program.** ~~~ ** Error message: *** Error: EvaluateExpression: Divide By Zero in EMS Program! *** ** ~~~ ** During Warmup, Environment=CHICAGO ANN HTG 99.6% CONDNS DB HVAC Sizing Pass 1, at Simulation time=01/21 00:00 - 00:01 ** Fatal ** Previous EMS error caused program termination.After I solved the severe error at the start of the simulation, I got another severe error of "Plant temperatures are getting far too hot" and the simulation terminated again. In conlusion, I solved the error by using "Outdoor air wet-bulb temperature + 3.6ºC" instead of Condenser water supply side outlet temperature, which is shown in the line A9 of
EnergyManagementSystem:Program. 3.6ºC is the Approach of cooling towers in my case which is set inSetpointManager:FollowOutdoorAirTemperature. The lines A8 and A9 ofEnergyManagementSystem:Programis to ensure that the condenser water temperature does not fall below the minimum temperature (5ºC). Using@MINis to ensure that the condenser water pump flow rate does not exceed the pump design flow rate (963.8kg/s). Using@MAXis to ensure that the condenser water pump flow rate does not fall below the minimum pump flow rate (20.075kg/s).Minimum Flow Rate FractioninHeaderedPumps:VariableSpeeddoes not work when EMS overrides the pump flow rate.** Severe ** Plant temperatures are getting far too hot, check controls and relative loads and capacities ** ~~~ ** During Warmup, Environment=CHICAGO ANN HTG 99.6% CONDNS DB HVAC Sizing Pass 1, at Simulation time=01/21 07:15 - 07:30 ** ~~~ ** PlantLoop Name (Demand Side) = CHWLOOP CONDENSER WATER LOOP ** ~~~ ** PlantLoop Setpoint Temperature=5.0 {C} ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Supply) does not have a Setpoint. ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Supply) has a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has temperature=322.2 {C} ** ~~~ ** PlantLoop Inlet Node (DemandSide) "CHWLOOP CNDW DEMAND INLET" has temperature=4.4 {C} ** ~~~ ** PlantLoop Minimum Temperature=5.0 {C} ** ~~~ ** PlantLoop Maximum Temperature=80.0 {C} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Supply)=0.0 {kg/s} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Demand)=959.7 {kg/s} ** ~~~ ** PlantLoop Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has mass flow rate =4.4E-002 {kg/s}UPDATE: I added the lines A6 and A7. It's not in this energy model, but I got the severe error of "Plant temperatures are getting far too hot". These two lines are to ensure that the condenser water flow rate quickly increases to the maximum (the pump design flow rate) when the condenser water temperature unexpectedly spikes.
This new feature requsest of variable condenser water flow rate has been abandoned for a long time. Hope it will be added to EnergyPlus soon.
Site_OA_WB, !- Name
ELSE, !- A10
ENDIF; !- A12
The annual electricity end uses are -51.4% -64.6% condenser water pump, +8.8% +1.7% heat rejection, +0.3% +1.7% cooling, and -0.1% +0.0% chilled water pump in my case. pump. The total end use of above 4 categories is -10.3%. -13.0%. No increase in the cooling unmet hours.
I had to use
Site_OA_WB, !- Name
ELSEIF CndW_Demand_Outlet_Temp CndW_Supply_Inlet_Temp >= 40, !- A6
SET CndW_Supply_Pump_Mass_Flow = @MIN (@MAX 20.075 963.8 (ChW_Supply_Cooling_Demand * 1.25 / 4180 / (CndW_Supply_Inlet_Temp - 5))) 963.8, 5)), !- A9
ELSE, !- A10
SET CndW_Supply_Pump_Mass_Flow = @MIN (@MAX 20.075 963.8 (ChW_Supply_Cooling_Demand * 1.25 / 4180 / (CndW_Supply_Inlet_Temp - (Site_OA_WB + 3.6)))) 963.8, 3.6))), !- A11
ENDIF; !- A12
The annual electricity end uses are -64.6% -56.5% condenser water pump, +1.7% +5.7% heat rejection, +1.7% -1.3% cooling, and +0.0% -0.3% chilled water pump. The total end use of above 4 categories is -13.0%. -12.7%. No increase in the cooling unmet hours.
I had to use
EnergyManagementSystem:Program. 3.6ºC is the Approach of cooling towers in my case which is set inSetpointManager:FollowOutdoorAirTemperature. The lines A8 and A9 ofEnergyManagementSystem:Programis to ensure that the condenser water temperature does not fall below the minimum temperature (5ºC).UsingUsing@MINis to ensure that the condenserwaterpump water flow rate does not exceed the pump design flow rate (963.8kg/s).UsingThese codes may not@MAXis to ensure that the condenser water pump flow rate doesfall below the minimum pump flow rate (20.075kg/s).be necessary.Minimum Flow Rate FractioninHeaderedPumps:VariableSpeeddoes not work when EMS overrides the pump flow rate.** Severe ** Plant temperatures are getting far too hot, check controls and relative loads and capacities ** ~~~ ** During Warmup, Environment=CHICAGO ANN HTG 99.6% CONDNS DB HVAC Sizing Pass 1, at Simulation time=01/21 07:15 - 07:30 ** ~~~ ** PlantLoop Name (Demand Side) = CHWLOOP CONDENSER WATER LOOP ** ~~~ ** PlantLoop Setpoint Temperature=5.0 {C} ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Supply) does not have a Setpoint. ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Supply) has a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has temperature=322.2 {C} ** ~~~ ** PlantLoop Inlet Node (DemandSide) "CHWLOOP CNDW DEMAND INLET" has temperature=4.4 {C} ** ~~~ ** PlantLoop Minimum Temperature=5.0 {C} ** ~~~ ** PlantLoop Maximum Temperature=80.0 {C} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Supply)=0.0 {kg/s} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Demand)=959.7 {kg/s} ** ~~~ ** PlantLoop Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has mass flow rate =4.4E-002 {kg/s}UPDATE: I added the lines A6 and A7. It's not in this energy model, but I got the severe error of "Plant temperatures are getting far too hot". These two lines are to ensure that the condenser water flow rate quickly increases to the maximum (the pump design flow rate) when the condenser water temperature unexpectedly spikes.
Surprisingly, EnergyPlus still lacks a feature of variable condenser water flow feature as of V23-2-0. I referred to @Julien Marrec and @Gio 's 4 year old answers.
Site_OA_WB, !- Name
ELSEIF CndW_Supply_Inlet_Temp >= 40, !- A6
SET CndW_Supply_Pump_Mass_Flow = @MIN 963.8 (ChW_Supply_Cooling_Demand * 1.25 / 4180 / (CndW_Supply_Inlet_Temp - 5)), !- A9
ELSE, !- A10
SET CndW_Supply_Pump_Mass_Flow = @MIN 963.8 (ChW_Supply_Cooling_Demand * 1.25 / 4180 / (CndW_Supply_Inlet_Temp - (Site_OA_WB + 3.6))), !- A11
ENDIF; !- A12
The annual electricity end uses are -56.5% condenser water pump, +5.7% heat rejection, -1.3% cooling, and -0.3% chilled water pump. The total end use of above 4 categories is -12.7%. No increase in the cooling unmet hours.
I had to use
EnergyManagementSystem:Program. 3.6ºC is the Approach of cooling towers in my case which is set inSetpointManager:FollowOutdoorAirTemperature. The lines A8 and A9 ofEnergyManagementSystem:Programis to ensure that the condenser water temperature does not fall below the minimum temperature (5ºC). Using@MINis to ensure that the condenser pump water flow rate does not exceed the pump design flow rate (963.8kg/s). These codes may not be necessary.** Severe ** Plant temperatures are getting far too hot, check controls and relative loads and capacities ** ~~~ ** During Warmup, Environment=CHICAGO ANN HTG 99.6% CONDNS DB HVAC Sizing Pass 1, at Simulation time=01/21 07:15 - 07:30 ** ~~~ ** PlantLoop Name (Demand Side) = CHWLOOP CONDENSER WATER LOOP ** ~~~ ** PlantLoop Setpoint Temperature=5.0 {C} ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Supply) does not have a Setpoint. ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Supply) has a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has temperature=322.2 {C} ** ~~~ ** PlantLoop Inlet Node (DemandSide) "CHWLOOP CNDW DEMAND INLET" has temperature=4.4 {C} ** ~~~ ** PlantLoop Minimum Temperature=5.0 {C} ** ~~~ ** PlantLoop Maximum Temperature=80.0 {C} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Supply)=0.0 {kg/s} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Demand)=959.7 {kg/s} ** ~~~ ** PlantLoop Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has mass flow rate =4.4E-002 {kg/s}UPDATE: I added the lines A6 and A7. It's not in this energy model, but I got the severe error of "Plant temperatures are getting far too hot". These two lines are to ensure that the condenser water flow rate quickly increases to the maximum (the pump design flow rate) when the condenser water temperature unexpectedly spikes.
Site_OA_WB, !- Name
A6
A7
ELSE, !- A10
A8
A9
ENDIF; !- A12
A10
I had to use
Plant Supply Side Cooling Demand Rate[W] of Chilled water loop instead of Condenser water loop to calculatePump Mass Flow Rateof the condenser water pump. When I usedPlant Supply Side Cooling Demand Rate[W] of Condenser water loop, it became zero andPump Mass Flow Rateof the condenser water pump became zero as well. The simulation did not terminate, but I got thousands of unmet hours as the cooling load was not handled. I could not identify the cause, but there may be something wrong during warmup. When I usedPlant Supply Side Cooling Demand Rate[W] of Chilled water loop, I multiplied 1.25, which is shown in the linesA9A7 andA11A9 ofEnergyManagementSystem:Program. It is becauseOutput:variables showed that Condenser water cooling demand rate is around 25% larger than Chilled water cooling demand rate on average, which is aligned with this discription in I/O Reference.The equation of mass flow rate that Julien showed could not be used as it is. The simulation starts with the minimum water temperature for both inlet and outlet i.e., TEWT = TLWT. The denominator of the equation becomes zero at the start of the simulation. I got the following severe error and the simulation terminated. I wanted to avoid the severe error above, but I needed to drive the condenser water pump at the start of the simulation. So, I have set the constant condenser water pump flow rate (80.3kg/s which is equal to the smallest pump of 6 pumps in bank) when the condenser water loop supply inlet temperature is 5ºC which is the
Minimum Loop TemperatureofCondenserLoopin my case. The code is shown in the lineA4A4 andA5A5 ofEnergyManagementSystem:Program.** ~~~ ** Error message: *** Error: EvaluateExpression: Divide By Zero in EMS Program! *** ** ~~~ ** During Warmup, Environment=CHICAGO ANN HTG 99.6% CONDNS DB HVAC Sizing Pass 1, at Simulation time=01/21 00:00 - 00:01 ** Fatal ** Previous EMS error caused program termination.After I solved the severe error at the start of the simulation, I got another severe error of "Plant temperatures are getting far too hot" and the simulation terminated again. In conlusion, I solved the error by using "Outdoor air wet-bulb temperature + 3.6ºC" instead of Condenser water supply side outlet temperature, which is shown in the line A9 of
EnergyManagementSystem:Program. 3.6ºC is the Approach of cooling towers in my case which is set inSetpointManager:FollowOutdoorAirTemperature. The linesA8 and A9A6 an A7 ofEnergyManagementSystem:Programis to ensure that the condenser water temperature does not fall below the minimum temperature (5ºC). Using@MINis to ensure that the condenser pump water flow rate does not exceed the pump design flow rate (963.8kg/s). These codes may not be necessary.** Severe ** Plant temperatures are getting far too hot, check controls and relative loads and capacities ** ~~~ ** During Warmup, Environment=CHICAGO ANN HTG 99.6% CONDNS DB HVAC Sizing Pass 1, at Simulation time=01/21 07:15 - 07:30 ** ~~~ ** PlantLoop Name (Demand Side) = CHWLOOP CONDENSER WATER LOOP ** ~~~ ** PlantLoop Setpoint Temperature=5.0 {C} ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Supply) does not have a Setpoint. ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Supply) has a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has temperature=322.2 {C} ** ~~~ ** PlantLoop Inlet Node (DemandSide) "CHWLOOP CNDW DEMAND INLET" has temperature=4.4 {C} ** ~~~ ** PlantLoop Minimum Temperature=5.0 {C} ** ~~~ ** PlantLoop Maximum Temperature=80.0 {C} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Supply)=0.0 {kg/s} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Demand)=959.7 {kg/s} ** ~~~ ** PlantLoop Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has mass flow rate =4.4E-002 {kg/s}UPDATE: I added the lines A6 and A7. It's not in this energy model, but I got the severe error of "Plant temperatures are getting far too hot". These two lines are to ensure that the condenser water flow rate quickly increases to the maximum (the pump design flow rate) when the condenser water temperature unexpectedly spikes.
Site_OA_WB, !- Name
ELSEIF Site_OA_WB <= 1.4, !- A6
SET CndW_Supply_Pump_Mass_Flow = @MIN 963.8 (ChW_Supply_Cooling_Demand * 1.25 / 4180 / (CndW_Supply_Inlet_Temp - 5)), !- A7
ELSE, !- A8
SET CndW_Supply_Pump_Mass_Flow = @MIN 963.8 (ChW_Supply_Cooling_Demand * 1.25 / 4180 / (CndW_Supply_Inlet_Temp - (Site_OA_WB + 3.6))), !- A9
ENDIF; !- A10
The annual electricity end uses are -56.5% condenser water pump, +5.7% heat rejection, -1.3% cooling, and -0.3% chilled water pump. The total end use of above 4 categories is -12.7%. No increase in the cooling unmet hours.-12.7%.
I had to use
Plant Supply Side Cooling Demand Rate[W] of Chilled water loop instead of Condenser water loop to calculatePump Mass Flow Rateof the condenser water pump. When I usedPlant Supply Side Cooling Demand Rate[W] of Condenser water loop, it became zero andPump Mass Flow Rateof the condenser water pump became zero as well. The simulation did not terminate, but I got thousands of unmet hours as the cooling load was not handled. I could not identify the cause, but there may be something wrong during warmup. When I usedPlant Supply Side Cooling Demand Rate[W] of Chilled water loop, I multiplied 1.25, which is shown in the lines A7 and A9 ofEnergyManagementSystem:Program. It is becauseOutput:variables showed that Condenser water cooling demand rate is around 25% larger than Chilled water cooling demand rate on average, which is aligned with this discription in I/O Reference.The equation of mass flow rate that Julien showed
could notcannot be used as it is. The simulation starts with the minimum water temperature for both inlet and outlet i.e., TEWT = TLWT. The denominator of the equation becomes zero at the start of the simulation. I got the following severe error and the simulation terminated. I wanted to avoid the severe error above, but I needed to drive the condenser water pump at the start of the simulation. So, I have set the constant condenser water pump flow rate (80.3kg/s which is equal to the smallest pump of 6 pumps in bank) when the condenser water loop supply inlet temperature is 5ºC which is theMinimum Loop TemperatureofCondenserLoopin my case. The code is shown in the line A4 and A5 ofEnergyManagementSystem:Program.** ~~~ ** Error message: *** Error: EvaluateExpression: Divide By Zero in EMS Program! *** ** ~~~ ** During Warmup, Environment=CHICAGO ANN HTG 99.6% CONDNS DB HVAC Sizing Pass 1, at Simulation time=01/21 00:00 - 00:01 ** Fatal ** Previous EMS error caused program termination.After I solved the severe error at the start of the simulation, I got another severe error of "Plant temperatures are getting far too hot" and the simulation terminated again. In conlusion, I solved the error by using "Outdoor air wet-bulb temperature + 3.6ºC" instead of Condenser water supply side outlet temperature, which is shown in the line A9 of
EnergyManagementSystem:Program. 3.6ºC is the Approach of cooling towers in my case which is set inSetpointManager:FollowOutdoorAirTemperature. The lines A6 an A7 ofEnergyManagementSystem:Programis to ensure that the condenser water temperature does not fall below the minimum temperature (5ºC). Using@MINis to ensure that the condenser pump water flow rate does not exceed the pump design flow rate (963.8kg/s). These codes may not be necessary.** Severe ** Plant temperatures are getting far too hot, check controls and relative loads and capacities ** ~~~ ** During Warmup, Environment=CHICAGO ANN HTG 99.6% CONDNS DB HVAC Sizing Pass 1, at Simulation time=01/21 07:15 - 07:30 ** ~~~ ** PlantLoop Name (Demand Side) = CHWLOOP CONDENSER WATER LOOP ** ~~~ ** PlantLoop Setpoint Temperature=5.0 {C} ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Supply) does not have a Setpoint. ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Supply) has a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has temperature=322.2 {C} ** ~~~ ** PlantLoop Inlet Node (DemandSide) "CHWLOOP CNDW DEMAND INLET" has temperature=4.4 {C} ** ~~~ ** PlantLoop Minimum Temperature=5.0 {C} ** ~~~ ** PlantLoop Maximum Temperature=80.0 {C} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Supply)=0.0 {kg/s} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Demand)=959.7 {kg/s} ** ~~~ ** PlantLoop Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has mass flow rate =4.4E-002 {kg/s}
Site_OA_WB, !- Name
ELSE, !- A8
ENDIF; !- A10
I had to use
Plant Supply Side Cooling Demand Rate[W] of Chilled water loop instead of Condenser water loop to calculatePump Mass Flow Rateof the condenser water pump. When I usedPlant Supply Side Cooling Demand Rate[W] of Condenser water loop, it became zero andPump Mass Flow Rateof the condenser water pump became zero as well. The simulation did not terminate, but I got thousands of unmet hours as the cooling load was not handled. I could not identify the cause, but there may be something wrong during warmup. When I usedPlant Supply Side Cooling Demand Rate[W] of Chilled water loop, I multiplied 1.25, which is shown in the lines A7 and A9 ofEnergyManagementSystem:Program. It is becauseOutput:variables showed that Condenser water cooling demand rate is around 25% larger than Chilled water cooling demand rate on average, which is aligned with this discription in I/O Reference.The equation of mass flow rate that Julien showed cannot be used as it is. The simulation starts with the minimum water temperature for both inlet and outlet i.e., TEWT = TLWT. The denominator of the equation becomes zero at the start of the simulation. I got the following severe error and the simulation terminated. I wanted to avoid the severe error above, but I needed to drive the condenser water pump at the start of the simulation. So, I have set the constant condenser water pump flow rate (80.3kg/s which is equal to the smallest pump of 6 pumps in bank) when the condenser water loop supply inlet temperature is 5ºC which is the
EnergyManagementSystem:Program. 3.6ºC is the Approach of cooling towers in my case which is set inSetpointManager:FollowOutdoorAirTemperature. The lines A6 an A7 ofEnergyManagementSystem:Programis to ensure that the condenser water temperature does not fall below the minimum temperature (5ºC). Using@MINis to ensure that the condenser pump water flow rate does not exceed the pump design flow rate (963.8kg/s). These codes may not be necessary.** Severe ** Plant temperatures are getting far too hot, check controls and relative loads and capacities ** ~~~ ** During Warmup,Environment=CHICAGOEnvironment=WUHAN ANN HTG 99.6% CONDNS DB HVAC Sizing Pass 1, at Simulation time=01/21 07:15 - 07:30 ** ~~~ ** PlantLoop Name (Demand Side) = CHWLOOP CONDENSER WATER LOOP ** ~~~ ** PlantLoop Setpoint Temperature=5.0 {C} ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Supply) does not have a Setpoint. ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Supply) has a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has temperature=322.2 {C} ** ~~~ ** PlantLoop Inlet Node (DemandSide) "CHWLOOP CNDW DEMAND INLET" has temperature=4.4 {C} ** ~~~ ** PlantLoop Minimum Temperature=5.0 {C} ** ~~~ ** PlantLoop Maximum Temperature=80.0 {C} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Supply)=0.0 {kg/s} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Demand)=959.7 {kg/s} ** ~~~ ** PlantLoop Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has mass flow rate =4.4E-002 {kg/s}
Site_OA_WB, !- Name
ELSE, !- A8
ENDIF; !- A10
I had to use
EnergyManagementSystem:Program. 3.6ºC is the Approach of cooling towers in my case which is set inSetpointManager:FollowOutdoorAirTemperature. The lines A6 an A7 ofEnergyManagementSystem:Programis to ensure that the condenser water temperature does not fall below the minimum temperature (5ºC). Using@MINis to ensure that the condenser pump water flow rate does not exceed the pump design flow rate (963.8kg/s). These codes may not be necessary.** Severe ** Plant temperatures are getting far too hot, check controls and relative loads and capacities ** ~~~ ** During Warmup, Environment=WUHAN ANN HTG 99.6% CONDNS DB HVAC Sizing Pass 1, at Simulation time=01/21 07:15 - 07:30 ** ~~~ ** PlantLoop Name (Demand Side) = CHWLOOP CONDENSER WATER LOOP ** ~~~ ** PlantLoop Setpoint Temperature=5.0 {C} ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Supply) does not have a Setpoint. ** ~~~ ** PlantLoop Inlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Supply) has a Setpoint. ** ~~~ ** PlantLoop Outlet Node (LoopSideLocation::Demand) does not have a Setpoint. ** ~~~ ** PlantLoop Outlet Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has temperature=322.2 {C} ** ~~~ ** PlantLoop Inlet Node (DemandSide) "CHWLOOP CNDW DEMAND INLET" has temperature=4.4 {C} ** ~~~ ** PlantLoop Minimum Temperature=5.0 {C} ** ~~~ ** PlantLoop Maximum Temperature=80.0 {C} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Supply)=0.0 {kg/s} ** ~~~ ** PlantLoop Flow Request (LoopSideLocation::Demand)=959.7 {kg/s} ** ~~~ ** PlantLoop Node (DemandSide) "CHWLOOP CNDW DEMAND OUTLET" has mass flow rate =4.4E-002 {kg/s}