AirTerminal:SingleDuct:ConstantVolume:CooledBeam
requires air inlet and outlet nodes even if you select Passive
for Cooled Beam Type
. If you want to supply fresh air with another AirLoop (CAV with Reheat), please set Supply Air Volumetric Flow Rate
0m3/s.
You can model multiple AirLoops serving a single thermal zone. So, one zone can have AirTerminal:SingleDuct:ConstantVolume:CooledBeam
and AirTerminal:SingleDuct:ConstantVolume:Reheat
. You should take care of how to input ZoneHVAC:EquipmentConnections
. One zone has only one Zone Air Inlet Node or NodeList Name
and one Zone Return Air Node or NodeList Name
. You need to use NodeList
Example:
ZoneHVAC:EquipmentConnections,
Zone_1, !- Zone Name
Zone_1 Equipment, !- Zone Conditioning Equipment List Name
Zone_1 Supply Inlets, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
Zone_1 Zone Air Node, !- Zone Air Node Name
Zone_1 Return Outlets; !- Zone Return Air Node or NodeList Name
NodeList,
Zone_1 Supply Inlets, !- Name
Zone_1 CooledBeam Supply Inlet, !- Node 1 Name
Zone_1 CAV Supply Inlet; !- Node 2 Name
NodeList,
Zone_1 Return Outlets, !- Name
Zone_1 CooledBeam Return Outlet, !- Node 1 Name
Zone_1 CAV Return Outlet; !- Node 2 Name