I think what @Yingying Tai wants to model is as follows.
I also want to model the thermostat control because it is specified in ANSI/ASHRAE/IES Standard 90.1 Performance Rating Method Reference Manual.
However, as @Aaron Boranian answered, ZoneControl:Thermostat:StagedDualSetpoint
has limited applicability. It is not for all types of HVAC system. Then, another option is to use Temperature Difference Between Cutout and Setpoint
in ZoneControl:Thermostat
, but the problem is that Temperature Difference Between Cutout and Setpoint
does not have a deadband above a cooling setpoint. The thermostat control would be as follows. That's not what @Yingying Tai and I expect.
I'm thinking of one makeshift. Temperature Difference Between Cutout and Setpoint
is set to 1deltaºC, and ThermostatSetpoint:SingleCooling
is changed from 24ºC to 24.5ºC. Then, the thermostat control would be as follows. It's pretty much what @Yingying Tai and I expect, but there is another problem. For unmet hours, Tolerance for Time Cooling Setpoint Not Met
is based on the thermostat setpoint, so the setting below would report so many unmet hours.
needs to be set to 1deltaºC as follows.
Nov 2023
I revised the second chart. The range of "Tolerance for Time Cooling Setpoint Not Met" was incorrect.
Nov 2023
Nov 2023