Use a SetpointManager:Scheduled set to ~55F on the supply outlet node if you want constant supply air temp, or a SetpointManager:Warmest:TempAndFlow if you want to have supply air temp reset based on the worst-case zone. In either case, the supply air temp will be cold, and any necessary reheat will be done by the zone terminals, not the central heating coil. The SetpointManager:SingleZone:Reheat is only used for single zone systems, where the reheat is done at the central heating coil (instead of at a terminal).