80 seems unrealistic and I think the same type of equipment should be combined first, but anyway you can edit Energy+.idd file in your local folder to extend the limitation.
If you are using EnergyPlusV22-2-0, probably the location of your idd file is C:\EnergyPlusV22-2-0
You can use any text editor tool and open the idd file. If you search "ZoneHVAC:EquipmentList", you can find the following description:
!*****************ZONE EQUIPMENT SPECIFICATION*********************
!Zone Heating and Cooling Equipment are attached to zones by the following statements:
ZoneHVAC:EquipmentList,
\extensible:6 Duplicate the six fields Zone Equipment Object Type through Sequential Heating Fraction
This class is extensible. You can copy from A3 to A6.
A3 , \field Zone Equipment 1 Object Type
\begin-extensible
\type choice
\key ZoneHVAC:TerminalUnit:VariableRefrigerantFlow
\key ZoneHVAC:AirDistributionUnit
\key ZoneHVAC:EnergyRecoveryVentilator
\key ZoneHVAC:EvaporativeCoolerUnit
\key ZoneHVAC:HybridUnitaryHVAC
\key ZoneHVAC:ForcedAir:UserDefined
\key ZoneHVAC:FourPipeFanCoil
\key ZoneHVAC:OutdoorAirUnit
\key ZoneHVAC:PackagedTerminalAirConditioner
\key ZoneHVAC:PackagedTerminalHeatPump
\key ZoneHVAC:UnitHeater
\key ZoneHVAC:UnitVentilator
\key ZoneHVAC:VentilatedSlab
\key ZoneHVAC:WaterToAirHeatPump
\key ZoneHVAC:WindowAirConditioner
\key ZoneHVAC:Baseboard:RadiantConvective:Electric
\key ZoneHVAC:Baseboard:RadiantConvective:Water
\key ZoneHVAC:Baseboard:RadiantConvective:Steam
\key ZoneHVAC:CoolingPanel:RadiantConvective:Water
\key ZoneHVAC:Baseboard:Convective:Electric
\key ZoneHVAC:Baseboard:Convective:Water
\key ZoneHVAC:HighTemperatureRadiant
\key ZoneHVAC:LowTemperatureRadiant:VariableFlow
\key ZoneHVAC:LowTemperatureRadiant:ConstantFlow
\key ZoneHVAC:LowTemperatureRadiant:Electric
\key ZoneHVAC:Dehumidifier:DX
\key ZoneHVAC:IdealLoadsAirSystem
\key ZoneHVAC:RefrigerationChillerSet
\key Fan:ZoneExhaust
\key WaterHeater:HeatPump:PumpedCondenser
\key WaterHeater:HeatPump:WrappedCondenser
\key HeatExchanger:AirToAir:FlatPlate
\key AirLoopHVAC:UnitarySystem
\required-field
A4 , \field Zone Equipment 1 Name
\required-field
\type object-list
\object-list ZoneEquipmentNames
N1 , \field Zone Equipment 1 Cooling Sequence
\required-field
\type integer
\minimum 0
\note Specifies the zone equipment simulation order
\note when the zone thermostat requests cooling
N2 , \field Zone Equipment 1 Heating or No-Load Sequence
\required-field
\type integer
\minimum 0
\note when the zone thermostat requests heating or no load
A5 , \field Zone Equipment 1 Sequential Cooling Fraction Schedule Name
\note The fraction of the remaining cooling load this equipment will attempt to serve
\note if the load distribution scheme is SequentialLoad, otherwise ignored.
\type object-list
\object-list ScheduleNames
A6 , \field Zone Equipment 1 Sequential Heating Fraction Schedule Name
\note The fraction of the remaining heating load this equipment will attempt to serve
\type object-list
By default, the last line of ZoneEquipmentList is A74. You can paste the copied A3 to A6 after the line A74, and please change the line number of the pasted lines accordingly i.e. A3→A75, A4→A76, N1→N37, N2→A38, A5→A77 and A6→A78.
Besides, you should change "Zone Equipment 1" in the pasted lines to "Zone Equipment 19".
And the most important thing is that you need to change comma (,) and semicolon(;). By default, the last line is as follows.
A74; \field Zone Equipment 18 Sequential Heating Fraction Schedule Name
\type object-list
You need to change the semicolon after A74 to comma i.e.
A74, \field Zone Equipment 18 Sequential Heating Fraction Schedule Name
\type object-list
Furthermore, you need to change the comma after the last line (A78 here) to semicolon i.e.
A78; \field Zone Equipment 19 Sequential Heating Fraction Schedule Name
\type object-list
Then, IDF Editor will show input fields for Zone Equipment 19. Please add more equipment in the same way if you want to. Again, the important thing is that semicolon should be only on the last line of the class.
\begin-extensible
\type choice
\required-field
\required-field
\type object-list
\required-field
\type integer
\minimum 0
\required-field
\type integer
\minimum 0
\type object-list
\type object-list
\type object-list
\type object-list
Furthermore, you need to change the comma after the last line (A78 (A80 here) to semicolon i.e.
A78; \field Zone Equipment 19 1 Sequential Heating Fraction Schedule Name
\type object-list
80 seems unrealistic and I think the same type of equipment should be combined first, but anyway you You can edit Energy+.idd file in your local folder to extend the limitation.
\begin-extensible
\type choice
\required-field
\required-field
\type object-list
\required-field
\type integer
\minimum 0
\required-field
\type integer
\minimum 0
\type object-list
\type object-list
\type object-list
\type object-list
Furthermore, you need to change the comma after the last line (A80 here) to semicolon i.e.
A78; \field Zone Equipment 1 Sequential Heating Fraction Schedule Name
\type object-list
