Thank you @Boranian for you answer,
I used the example you mentioned above and adapted it to my problem, I also set the temperature difference between cutoff and setpoint to 4C as you said, but unfortunately this does not work and gives the following error.
* Severe * DualSetPointWithDeadBand: When Temperature Difference Between Cutout And Setpoint is applied, the heating setpoint is greater than the cooling setpoint.
* ~~~ * occurs in Zone=WALK-IN ZONE During Warmup, Environment=RUN PERIOD, at Simulation time=08/10 00:00 - 00:03
* ~~~ * Zone Heating ThermostatSetPoint=-22.00
* ~~~ * Zone Cooling ThermostatSetPoint=-22.00
* Fatal * Program terminates due to above conditions.
I then changed the value of the temperature difference between cutoff and setpoint to 3C and the result was not what I expected (figure below), as you can see, the temperature fluctuations are not steady and the temperature does not reach the two defined values -18°C and -22°C.
UPDATES
This is the result after I changed the outputs frequency from Timestep to Detailed.
UPDATES
This is the result after I changed the outputs frequency from Timestep to Detailed. The cutoff is set to 3C
UPDATES
The cutoff is set to 3CDetailed
UPDATES
Thank you @Boranian @Aaron for you answer,
Thank you @Aaron for you answer,