In the Fan:VariableVolume object are coefficients for how power varies with flow. Set up these coefficients to provide a cubed output of power versus flow. At a flow fraction of 1, this curve output should be 1. At a flow fraction of 0.5 this curve output should be 0.125. Set coefficient 4 = 1 and the others = 0. Note that Coeff 1 = constant, Coeff 2 = flow fraction, Coeff 3 = flow fraction^2, Coeff 4 = flow fraction^3 and Coeff 5 = flow fraction ^4. So for an ideal fan only Coeff 4 is used.
Fan:VariableVolume,
  N8 , \field Fan Power Coefficient 1
       \note all Fan Power Coefficients should not be 0.0 or no fan power will be consumed.
       \note Fan Power Coefficents are specified as function of full flow rate/power
       \note Equation:
  N9 , \field Fan Power Coefficient 2
  N10, \field Fan Power Coefficient 3
  N11, \field Fan Power Coefficient 4
  N12, \field Fan Power Coefficient 5
