I've made the change you indicated and tested with the latest release (22.1) and with my build of the in-development code. In both cases I am getting warnings, but the simulation completes. What EnergyPlus version are you using and what weather file? I wouldn't say my simulations are successful, there are 1000+ warnings about low flows and out-of-range temperatures, here's an example:
************* ** Warning ** HeatExchanger:AirToAir:SensibleAndLatent "OA HEAT RECOVERY 1": Average air volume flow rate is <50% or >130% warning continues. Air flow rate ratio statistics follow.
************* ** ~~~ ** This error occurred 824 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=0.115243 Min=0.115243
I would not expect such a drastic change of a single field to work very well, there's a lot that can go wrong with that, especially when you're changing one of the design inputs that's really likely to clash with other inputs. If you do go through the process of changing other inputs to silence all the warnings, you're likely to end up with a different design and that's probably not what you want. I'm guessing it would be better to limit the flow another way that doesn't change the overall design. Why are you interested in such a low flow rate?
Update
Looking at your file, I see that you have lowered the flow rate in more places than I did. That accounts for why mine completed and yours did not. It appears that the pressure solution is driving things backwards in a sense, and it may be that the pressures here are just not compatible with a simulation of the distribution system with such low flow. There are still other issues that could be playing a role. If I take the original example file and change the "AirflowNetwork Control" field in the AirflowNetwork:SimulationControl
object from MultizoneWithDistribution
to NoMultizoneOrDistribution
, that simulation will complete and the only warnings are about unused AirflowNetwork objects being present and missing outputs. Both of those things make sense. If I take your file and do the same thing, I get a lot of warnings about low temperatures and such, so the HVAC is having a problem with the low flow rates. I also tried MultizoneWithoutDistribution
with similar results.
So, what to do? I think there are two options:
- If you can fix the warnings that are cropping up in the
simulation, then you can go back and try the AFN simulation and see what happens (with bothMultizoneWithDistribution
andMultizoneWithoutDistribution
). Keep in mind that the distribution simulation may still not work, but the results are now at least more defensible. The handling of fans in AFN is necessarily somewhat simplified, and while it's possible there's a bug lurking in here somewhere, the distribution solution just may not be able to handle the low flows in this model. - If you take a look at the results of the
simulation of your current model and find that gives you what you need, then you're done. The warnings are a bit worrisome (Outlet temperature = -652.61 C
) so I'd be careful about how I interpreted the results.
My preference would be the first option. If you can get the system sized correctly (you may be able to autosize the capacities to get rid of the coil issues), then that's going to change the temperatures, which will change the fluid properties, which changes the AFN solution. So all hope is not lost, I just felt I had to add that warning in the first option because the disparity in flow magnitudes is tough to handle.
If you have trouble getting the non-AFN model to work well with low flows, I'd suggest asking another question. There are experts in that part of the code that regularly answer questions here that would be able to help you get the system right.
Update
My preference would be the first option. If you can get the system sized correctly (you may be able to autosize the capacities to get rid of the coil issues), then that's going to change the temperatures, which will change the fluid properties, which with changes the AFN solution. So all hope is not lost, I just felt I had to add that warning in the first option because the disparity in flow magnitudes is tough to handle.
Update
My preference would be the first option. If you can get the system sized correctly (you may be able to autosize the capacities to get rid of the coil issues), then that's going to change the temperatures, which will change the fluid properties, with changes the AFN solution. So all hope is not lost, I just felt I had to add that warning in the first option because the disparity in flow magnitudes is tough to handle.
