Yes, you should be able to use any of the PlantEquipmentOperation:### objects with the PlantComponent:UserDefined object. The EMSUserDefined5ZoneAirCooled.idf example file that comes with EnergyPlus shows a case where a PlantComponent:UserDefined object represents a chiller, so it uses the PlantEquipmentOperation:CoolingLoad object to control how it meets chilled water loads. See an excerpt below for the plant loop and related operation scheme settings, with a "*" next to the important input fields making references between objects.
PlantLoop,
Chilled Water Loop, !- Name
Water, !- Fluid Type
, !- User Defined Fluid Type
* CW Loop Operation, !- Plant Equipment Operation Scheme Name
CW Supply Outlet Node, !- Loop Temperature Setpoint Node Name
98, !- Maximum Loop Temperature {C}
1, !- Minimum Loop Temperature {C}
autosize, !- Maximum Loop Flow Rate {m3/s}
0.0, !- Minimum Loop Flow Rate {m3/s}
, !- Plant Loop Volume {m3}
CW Supply Inlet Node, !- Plant Side Inlet Node Name
CW Supply Outlet Node, !- Plant Side Outlet Node Name
Cooling Supply Side Branches, !- Plant Side Branch List Name
Cooling Supply Side Connectors, !- Plant Side Connector List Name
CW Demand Inlet Node, !- Demand Side Inlet Node Name
CW Demand Outlet Node, !- Demand Side Outlet Node Name
Cooling Demand Side Branches, !- Demand Side Branch List Name
Cooling Demand Side Connectors, !- Demand Side Connector List Name
SequentialLoad, !- Load Distribution Scheme
CW Avail List; !- Availability Manager List Name
PlantEquipmentOperationSchemes,
CW Loop Operation, !- Name
* PlantEquipmentOperation:CoolingLoad, !- Control Scheme 1 Object Type
* Central Chiller Only, !- Control Scheme 1 Name
PlantOnSched; !- Control Scheme 1 Schedule Name
Central Chiller Only, !- Name
0, !- Load Range 1 Lower Limit {W}
900000, !- Load Range 1 Upper Limit {W}
* Cooling Plant; !- Range 1 Equipment List Name
PlantEquipmentList,
Cooling Plant, !- Name
* PlantComponent:UserDefined, !- Equipment 1 Object Type
* Central Chiller; !- Equipment 1 Name
More specifics about your controls need to be defined in the Plant Connection Loading Mode input field of the user-defined plant component, as well as the EMS programs used for initialization and simulation of the user-defined plant component.
Yes, you should be able to use any of the PlantEquipmentOperation:### objects with the PlantComponent:UserDefined object. The EMSUserDefined5ZoneAirCooled.idf example file that comes with EnergyPlus shows a case where a PlantComponent:UserDefined object represents a chiller, so it uses the PlantEquipmentOperation:CoolingLoad object to control how it meets chilled water loads. See an excerpt below for the plant loop and related operation scheme settings, with a "*" next to the important input fields making references between objects.for your question.
PlantLoop,
PlantEquipmentList,