It sounds like you want to use the logical "and" operator: &&
. You can read more about operators available for EMS in the Expressions section of the EMS Application Guide.
Also, I don't believe you need LoopWindowAttribute
, as the Month
and Hour
variables are already built in to EMS and not "attached" to specific EnergyPlus objects like windows. You can read more about built-in variables for EMS.
Using &&
and removing LoopWindowAttribute
, your EMS program would look like this:
NatVent,
<ForAllExternalWindows>
IF Zone_People_Occupant_Count_<LoopWindowVariableName> == 0,
SET Venting_Opening_Factor_<LoopWindowVariableName> = 0,
ELSEIF (Zone_People_Occupant_Count_<LoopWindowVariableName> > 0),
IF Month >=5 && Month <=9 && Hour >=7 && Hour <=9,
SET Venting_Opening_Factor_<LoopWindowVariableName> = 1,
ELSE,
SET Venting_Opening_Factor_<LoopWindowVariableName> = null,
ENDIF,
ENDIF,
<LoopNextWindow>
You also needed a second ENDIF
statement, since you have two IF