As an alternative you can use EMS programs with IDF editor:
(1) in OpenStudio, define setpoint manager with constant temperature schedule [e.g.: controlledTemp],
in preliminary scheme.
(2) in the generated out.idf insert an EMS sensor e.g. for outdoor drybulb temperature [sensor variable:
OutdoorTemp]
(3) define actuator on the temperature schedule [controlledTemp] e.g.:
myTempControl, !- Name
controlledTemp, !- Actuated Component Unique Name
Schedule:Constant, !- Actuated Component Type
Schedule Value; !- Actuated Component Control Type
(4) Define heating curve by EMS program, e.g.
myTempManager, !- Name
SET controlledTemp=-32/40*OutdoorTemp+49, !- Program Line 1
IF controlledTemp>65, !- Program Line 2
SET controlledTemp=65, !- A4
ENDIF; !- A5
(5) Declare EMS program(s) to be run in EMS Program Calling Manager:
myEMS Custom Controls, !- Name
EndOfZoneTimestepBeforeZoneReporting, !- EnergyPlus Model Calling Point
myTempManager, !- Program Name 1
This solution is the most flexible because you have full control over setting limits and logical conditions. And, as the example shows, it is done quickly with a few instructions.