Read the input/output reference manual section relative to People. You should also take a look at ASHRAE 55 directly. If you want to see how parameters affect whether it's comfortable or not, you can try the CBE Thermal Comfort Tool which is actually cited by the Input/Output reference.
Factors that come into play in the calculation:
- Operative temperature, taken as the average of the air temperature and the mean radiant temperature. ASHRAE 55-2004, appendix C, says that this is true if the relative air speed is small (<0.2 m/s, 40 fpm)
- All of these parameters under the People object:
- Clothing level (clo): typical is 0.5 in summer and 1.0 in winter
- Air velocity schedule
- Activity level (met): Metabolic rates, depends on the type of activity is done in the space, for example 1.0 for "seated, reading or writing", 1.2 for "filing, seated", or even 5 to 7.6 for basketball playing.
- Enable ASHRAE 55 comfort warnings: you have to enable which people objects you want to report comfort warnings.
Read the input/output reference manual section relative to People. People. You should also take a look at ASHRAE 55 directly.