If you want to have the same temperatures set by hour, and the day of the year is not important, then you can set the Through: input field of the Schedule:Compact objects to the end of the year (see below).
Schedule:Compact,
Heating Setpoint,
Any Number,
Through: 12/31,
For: Alldays,
Until: 7:00, 17.00,
Until: 23:00, 20.00,
Until: 24:00, 17.00;
This way, all days the whole year will follow the same schedule values -- you don't need to define them individually if they follow the same schedule value trends. The same idea also applies to your EMS programs -- if you only need to override setpoints based on hour of the day, then you don't need to include DayOfYear in your EMS program logic (see below).
RHuescaCfaCATIII2018OUTCTEACSTProg,
<ForAllOccupiedZones>
IF (CurrentTime < 7),
Set R_Huesca_Cfa_CATIII_2018_OUT_CTE_<LoopZoneVariableName>_FORSCRIPT_ACST = 27,
ELSEIF (CurrentTime < 15),
Set R_Huesca_Cfa_CATIII_2018_OUT_CTE_<LoopZoneVariableName>_FORSCRIPT_ACST = 50,
ELSEIF (CurrentTime < 23),
Set R_Huesca_Cfa_CATIII_2018_OUT_CTE_<LoopZoneVariableName>_FORSCRIPT_ACST = 25,
ELSEIF (CurrentTime < 24),
ENDIF;
If you want to have thermostat control based on operative temperature, I would make sure that you have DesignBuilder's calculation options set correctly for Temperature control. If you are using Simple HVAC then you only set a normal and setback temperature value for thermostats in the Activity tab-- a schedule is only used for the operation of HVAC equipment. For Detailed HVAC, you would select heating/cooling thermostat setpoint schedules for a zone in the HVAC diagram interface. If this all is set correctly, then I would double-check that EMS is overriding the same schedule name that you assigned to the heating/cooling thermostats in the zones.
Side question: If you're only overriding schedule values based on time, and not zone air temperatures or other items that EnergyPlus is calculating each timestep, then I don't think you need EMS at all -- you just need schedules. Unless I'm missing something here ...
UPDATE FOLLOWING COMMENT BELOW
If you want to update a schedule every day in DesignBuilder, and are limited by the number of lines you can define in its Schedule:Compact window, then you may want to examine defining this schedule in a CSV file. EnergyPlus can load external files to use as schedules through the Schedule:File object. While DesignBuilder cannot currently load full IDFs, it can load include "partial IDFs" to combine with the DesignBuilder model. So, if here is the process that I would recommend trying:
- Create the Schedule:File object in a partial IDF that reads in the external CSV file defining schedule values. The partial IDF needs to be saved in C:\Users\[Your Name]\AppData\Local\DesignBuilder\EnergyPlus, and the external CSV file likely needs to be in the same folder as well.
- Include that partial IDF into the DesignBuilder model
- Assign any schedule name to the thermostats in the DesignBuilder model (let's say T_stat_schedule, for example)
- Use EMS to read the Schedule:File values from the external CSV as a sensor
- Use EMS to use the schedule value actuator to reset the current thermostat schedule value (T_stat_schedule) to the Schedule:File value read by the EMS sensor
Schedule:Compact,
Heating Setpoint,
Any Number,
Through: 12/31,
For: Alldays,
Until: 7:00, 17.00,
ENDIF;