May I try it first again :).
If you created a dummy zone with a water convector I would set up an availability schedule for a water convector to 0 and than overwrite it by EMS as a function of loop temperature (for example you can use pump leaving temperature as a sensor node). EMS code should not be complex. It should look something like:
Schedule:Constant,AvailOff,On/Off,0; !- baseboard heater availability schedule
EnergyManagementSystem:Sensor, !- pump leaving water temperature node
PumpTemp,
HW Pump Out Node,
System Node Temperature;
EnergyManagementSystem:Actuator,
AvailSCH_Overwrite,
AvailOff,
Schedule:Constant,
Schedule Value;
Overwrite Example,
BeginTimestepBeforePredictor, !- You might need to use different EMS calling point here
OverwriteProg;
OverwriteProg,
IF PumpTemp > 80.5, !- I'm not sure what is the loop limit in your case, but you can add 0.5C over the limit to make a dummy heater switched on
Set AvailSCH_Overwrite = 1,
ELSE,
Set AvailSCH_Overwrite = 0,
ENDIF;
Cheers, IK
PumpTemp,
HW Pump Out Node,
AvailSCH_Overwrite,
AvailOff,
Schedule:Constant,
Schedule Value;
Overwrite Example,
OverwriteProg;
OverwriteProg,
IF PumpTemp > 80.5, 85.5, !- I'm not sure what is the loop limit in your case, but you can add 0.5C over the limit to make a dummy heater switched on
ELSE,
ENDIF;
Cheers, IK