I found your question because I have the same one. In Energy Plus, I was able to add a relief fan as a component on the AirLoopHVAC:OutdoorAirSystem, just by modifying the AirloopHVAC:OutdoorAirSystem:EquipmentList and adding the Relief fan object. I started with the expanded IDF from the example file "HVACTemplate-5ZoneVAVWaterCooled.idf". I checked the hourly output variables for the fan power and the node flow exiting the fan and it seems to work. Here are the objects I modified/added:
AirLoopHVAC:OutdoorAirSystem:EquipmentList,
VAV Sys 1 OA System Equipment, !- Name
OutdoorAir:Mixer, !- Component Object Type
VAV Sys 1 OA Mixing Box, !- Component Name
Fan:VariableVolume, !- Component Object Type
VAV Sys 1 Relief Fan; !- Component Name
Fan:VariableVolume,
VAV Sys 1 Relief Fan, !- Name
FanAvailSched, !- Availability Schedule Name
0.7, !- Fan Efficiency
600, !- Pressure Rise {Pa}
autosize, !- Maximum Flow Rate {m3/s}
Fraction, !- Fan Power Minimum Flow Rate Input Method
0.25, !- Fan Power Minimum Flow Fraction
, !- Fan Power Minimum Air Flow Rate {m3/s}
0.9, !- Motor Efficiency
1, !- Motor in Airstream Fraction
0.35071223, !- Fan Power Coefficient 1
0.30850535, !- Fan Power Coefficient 2
-0.54137364, !- Fan Power Coefficient 3
0.87198823, !- Fan Power Coefficient 4
0, !- Fan Power Coefficient 5
VAV Sys 1 Relief Air Outlet, !- Air Inlet Node Name
VAV Sys 1 Relief Fan Outlet; !- Air Outlet Node Name
I found your question because I have the same one. In Energy Plus, I was able to add a relief fan as a component on the AirLoopHVAC:OutdoorAirSystem, just by modifying the AirloopHVAC:OutdoorAirSystem:EquipmentList and adding the Relief fan object. I started with the expanded IDF from the example file "HVACTemplate-5ZoneVAVWaterCooled.idf". I checked the hourly output variables for the reports on fan power and the node flow exiting the fan and it seems to work. Here are the objects I modified/added:
Fan:VariableVolume,