If you will ask for output of the following variables:
Zone Air Temperature, Zone Thermostat Heating Setpoint Temperature and
and Zone Thermostat Cooling Setpoint Temperature
at hourly rate you will be able to calculate what ever you need.
For the hour of exceedance you can use those four output variables:
Zone Heating Setpoint Not Met Time
Zone Heating Setpoint Not Met While Occupied
Zone Cooling Setpoint Not Met Time
Zone Cooling Setpoint Not Met While Occupied Time
You can read about output variables in the Input Output Reference .
You can look at that result for the search I made in Google for weighted exceedance (We).
One more thing is that in OS at the OpenStudio Result Measure you will find few lines of the top the unmethours tolerance which I think by default is set to 0.37 deg R.