This is straightforward with the OpenStudio SDK.
Create a
ZoneHVACFourPipeFanCoil
object for each zone. Each FCU requires a schedule, fan, cooling coil, and a heating coil to create the object. The heating coil can be an electric resistance coil.
Example script:
require 'openstudio' # load the OpenStudio SDK
# logic to load the model in the current version of the SDK
osm_path = OpenStudio::Path.new("C:/Users/yourname/Desktop/model.osm")
translator = OpenStudio::OSVersion::VersionTranslator.new
model = translator.loadModel(osm_path)
model = model.get
# create an array of zones served by FCUs
zones = model.getThermalZones # this returns all zones in the model
# there are many other ways you can create an array of zones, e.g. by space names, zone names, from a .csv file, etc.
# for example, choose only zones with "served by FCU" in name
zones = zones.select {|zone| zone.name.to_s.include? "served by FCU"}
# reference a chilled water loop in your model
chilled_water_loop = model.getPlantLoopByName("Chilled Water Loop").get
# loop through each zone and add an FCU
zones.each do |zone|
# create a coil cooling water
clg_coil = OpenStudio::Model::CoilCoolingWater.new(model)
clg_coil.setName("#{zone.name.to_s} FCU Cooling Coil")
chilled_water_loop.addDemandBranchForComponent(clg_coil) # add to chilled water loop
clg_coil.setAvailabilitySchedule(model.alwaysOnDiscreteSchedule)
clg_coil.setHeatExchangerConfiguration('CrossFlow')
# set cooling coil design temperatures if desired
# clg_coil.setDesignInletWaterTemperature()
# clg_coil.setDesignInletAirTemperature()
# clg_coil.setDesignOutletAirTemperature()
# coil controller properties
clg_coil_controller = clg_coil.controllerWaterCoil.get
clg_coil_controller.setName("#{clg_coil.name.to_s} Controller")
clg_coil_controller.setMinimumActuatedFlow(0.0)
# create an electric heating coil
htg_coil = OpenStudio::Model::CoilHeatingElectric.new(model)
htg_coil.setName("#{zone.name.to_s} FCU Electric Heating Coil")
htg_coil.setAvailabilitySchedule(model.alwaysOnDiscreteSchedule)
htg_coil.setEfficiency(1.0)
# create a fan onoff
fan = OpenStudio::Model::FanOnOff.new(model)
fan.setName("#{zone.name.to_s} FCU Fan")
fan.setPressureRise(300.0) # pa
fan.setFanEfficiency(0.60)
fan.setMotorEfficiency(0.80)
fan.setMotorInAirstreamFraction(1.0)
fan.setEndUseSubcategory("FCU Fans")
fan.setAvailabilitySchedule(model.alwaysOnDiscreteSchedule)
fan.autosizeMaximumFlowRate
# create a fan coil unit with these objects
fcu = OpenStudio::Model::ZoneHVACFourPipeFanCoil.new(model,
model.alwaysOnDiscreteSchedule,
fan,
clg_coil,
htg_coil)
fcu.setName("#{zone.name} FCU")
fcu.setCapacityControlMethod('CyclingFan')
fcu.autosizeMaximumSupplyAirFlowRate
fcu.setMaximumOutdoorAirFlowRate(0.0) # no outdoor ventilation from FCUs
fcu.addToThermalZone(zone)
end
path = "C:/Users/yourname/Desktop/model_new.osm"
model.save(path,true)
The Prototype.hvac_system has plenty of examples for building all different kinds of HVAC systems. Use can use the methods directly with require 'openstudio-standards'
, or copy them into your own scripts.
See the OpenStudio measure writing guide if you'd like to expand this into an OpenStudio measure.
