The Create Baseline Building measure will handle this for you, which uses the coefficients below. These come from page 3.221 (251) of the PNNL 90.1-2010 Performance Rating Method Reference Manual (and probably from COMNET and Title24 references too).
case control_type
when 'Constant Flow'
coeff_a = 0.0
coeff_b = 1.0
coeff_c = 0.0
coeff_d = 0.0
when 'Riding Curve'
coeff_a = 0.0
coeff_b = 3.2485
coeff_c = -4.7443
coeff_d = 2.5294
when 'VSD No Reset'
coeff_a = 0.0
coeff_b = 0.5726
coeff_c = -0.301
coeff_d = 0.7347
when 'VSD DP Reset'
coeff_a = 0.0
coeff_b = 0.0205
coeff_c = 0.4101
coeff_d = 0.5753
Since the project is using the performance path you don't need to follow the prescriptive requirements of subsection 5, just the mandatory requirements of subsection 4.
G1.2 Performance Rating. This performance rating method requires conformance with the following provisions: All requirements of Sections 5.4, 6.4, 7.4, 8.4, 9.4, and 10.4 are met. These sections contain the mandatory provisions of the standard and are prerequisites for this rating method...
case control_type
coeff_a = 0.0
coeff_b = 1.0
coeff_c = 0.0
coeff_d = 0.0
when 'Riding Curve'
coeff_a = 0.0
coeff_b = 3.2485
coeff_c = -4.7443
coeff_d = 2.5294
when 'VSD No Reset'
coeff_a = 0.0
coeff_b = 0.5726
coeff_c = -0.301
coeff_d = 0.7347
when 'VSD DP Reset'
coeff_a = 0.0
coeff_b = 0.0205
coeff_c = 0.4101
coeff_d = 0.5753
Since the project is using the performance path you don't need to follow the prescriptive _prescriptive_ requirements of subsection 5, just the mandatory _mandatory_ requirements of subsection 4.
case control_type
coeff_a = 0.0
coeff_b = 1.0
coeff_c = 0.0
coeff_d = 0.0
when 'Riding Curve'
coeff_a = 0.0
coeff_b = 3.2485
coeff_c = -4.7443
coeff_d = 2.5294
when 'VSD No Reset'
coeff_a = 0.0
coeff_b = 0.5726
coeff_c = -0.301
coeff_d = 0.7347
when 'VSD DP Reset'
coeff_a = 0.0
coeff_b = 0.0205
coeff_c = 0.4101
coeff_d = 0.5753
Since the project is using the performance path you don't need to follow the _prescriptive_ "prescriptive" requirements of subsection 5, just the _mandatory_ mandatory requirements of subsection 4.
The Create Baseline Building measure will handle this for you, which uses use the coefficients below. These come from page 3.221 (251) of the PNNL 90.1-2010 Performance Rating Method Reference Manual (and probably from COMNET and Title24 references too).
case control_type
coeff_a = 0.0
coeff_b = 1.0
coeff_c = 0.0
coeff_d = 0.0
when 'Riding Curve'
coeff_a = 0.0
coeff_b = 3.2485
coeff_c = -4.7443
coeff_d = 2.5294
when 'VSD No Reset'
coeff_a = 0.0
coeff_b = 0.5726
coeff_c = -0.301
coeff_d = 0.7347
when 'VSD DP Reset'
coeff_a = 0.0
coeff_b = 0.0205
coeff_c = 0.4101
coeff_d = 0.5753
Since the project is using the performance path you don't need to follow the "prescriptive" requirements of subsection 5, just the mandatory requirements of subsection 4.
The Create Baseline Building measure will handle this for you, which use the coefficients below. These come from page 3.221 (251) of the PNNL 90.1-2010 Performance Rating Method Reference Manual (and probably from COMNET and Title24 references too).
case control_type
coeff_a = 0.0
coeff_b = 1.0
coeff_c = 0.0
coeff_d = 0.0
when 'Riding Curve'
coeff_a = 0.0
coeff_b = 3.2485
coeff_c = -4.7443
coeff_d = 2.5294
when 'VSD No Reset'
coeff_a = 0.0
coeff_b = 0.5726
coeff_c = -0.301
coeff_d = 0.7347
when 'VSD DP Reset'
coeff_a = 0.0
coeff_b = 0.0205
coeff_c = 0.4101
coeff_d = 0.5753
method...method. The improved performance of the proposed building design is calculated in accordance with provisions of this appendix using the following formula:
The Create Baseline Building measure will should handle this for you, which use but here are the coefficients below. These it uses, which come from page 3.221 (251) of the PNNL 90.1-2010 Performance Rating Method PRM Reference Manual (and probably from COMNET and Title24 references too). .
case control_type
coeff_a = 0.0
coeff_b = 1.0
coeff_c = 0.0
coeff_d = 0.0
when 'Riding Curve'
coeff_a = 0.0
coeff_b = 3.2485
coeff_c = -4.7443
coeff_d = 2.5294
when 'VSD No Reset'
coeff_a = 0.0
coeff_b = 0.5726
coeff_c = -0.301
coeff_d = 0.7347
when 'VSD DP Reset'
coeff_a = 0.0
coeff_b = 0.0205
coeff_c = 0.4101
coeff_d = 0.5753
G1.2 Performance Rating. This performance rating method requires conformance with the following provisions: All requirements of Sections 5.4, 6.4, 7.4, 8.4, 9.4, and 10.4 are met. These sections contain the mandatory provisions of the standard and are prerequisites for this rating method. The improved performance of the proposed building design is calculated in accordance with provisions of this appendix using the following formula:
