Your right. The documentation does show units of percent. Same for the next field of drift loss percent. A review of the code shows that the Evaporation Loss Factor field is currently a fraction, not percent, of water flow rate.
The IDD shows the same information described in the Input Output Reference document:
N19, \field Evaporation Loss Factor
\type real
\units percent/K
\note Rate of water evaporation from the cooling tower and lost to the outdoor air [%/K]
\note Evaporation loss is calculated as percentage of the circulating condenser water rate
\note Value entered here is percent-per-degree K of temperature drop in the condenser water
\note Typical values are from 0.15 to 0.27 [%/K].
\default 0.2
N20, \field Drift Loss Percent
\type real
\default 0.008
\units percent
\note Rate of drift loss as a percentage of circulating condenser water flow rate
\note Typical values are between 0.002 and 0.2% The default value is 0.008%
And the code where these data are read in shows:
SimpleTower( TowerNum ).UserEvapLossFactor = NumArray( 19 ); // N11 , \field Evaporation Loss Factor
SimpleTower( TowerNum ).DriftLossFraction = NumArray( 20 ) / 100.0; // N12, \field Drift Loss Percent