Sorry, this content is no longer available
Don't use a WaterUse:Equipment for this (this is something to model (typically hot) water usage at a faucet, all water used is replaced by mains water), but use a LoadProfile:Plant instead.
As far as on/off chillers, there aren't any specific objects to do this, in particular for "modular" type chillers that have several compressors. You could however use a Chiller:Electric:EIR and force the Minimum Part Load Ratio to something close to 1 to force your chiller to operate at rated capacity (haven't tested myself). Make sure you set the Minimum Unloading Ratio to the same value as the Min PLR.
If your chiller is of modular type, say with 3 identical compressors, you'd model three identical chillers corresponding to each compressor.
myself). If your chiller is of modular type, say with 3 identical compressors, you'd model three identical chillers corresponding to each compressor.