I found a solution that provides the following on the supply side of AirLoopHVAC:
- hot gas reheat for dehumidification
- variable airflow
- primary DX heating and cooling coils
- an additional supplementary heating coil
I achieved this by doing the following:
Created AirLoopHVAC:UnitarySystem with: - DX Heating Coil - DX Cooling Coil - Coil:Heating:Desuperheater for hot gas reheat - control type is "SetPoint" - if control type is "Load" fans do not operate at variable air volume
Added a Coil:Heating:Fuel to the outlet node of the AirLoopHVAC:UnitarySystem. The Coil:Heating:Fuel is also setpoint controlled.