VAV reheat coil undersizing in a known issue. One workaround could be to reduce Central Heating Design Supply Air Temperature (to 14 or 13.5 in this case). That will increase the design heating load on reheat coil and reduce the unmet heating hours in core zone. Other approach could be to add fictitious heating load only during winter design day (Central Heating Design Supply Air Temperature will be unchanged) as illustrated below.
Schedule:Compact,
Other Equipment Schedule, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: WinterDesignDay, !- Field 2
Until: 24:00, !- Field 3
1, !- Field 4
For: AllOtherDays, !- Field 5
Until: 24:00, 0; !- Field 6
OtherEquipment,
Level1XGroundLevelX:OfficeSpaceXCoreX Other Equip, !- Name
None, !- Fuel Type
Level1XGroundLevelX:OfficeSpaceXCoreX, !- Zone or ZoneList Name
Other Equipment Schedule, !- Schedule Name
Watts/Area, !- Design Level Calculation Method
, !- Design Level {W}
-20, !- Power per Zone Floor Area {W/m2}
, !- Power per Person {W/Person}
0, !- Fraction Latent
0, !- Fraction Radiant
0; !- Fraction Lost