Once you run a model with HVACTemplate objects, it is a good idea to verify the inputs in the expidf to make sure that the inputs in the HVACTemplate objects get translated as desired.
I would suggest that you make a copy of the expidf and verify all inputs related to flowrates of the following objects:
DesignSpecification:OutdoorAir
- just to make sure that the OA flowrates are modelled accurately;
AirTerminal:SingleDuct:VAV:Reheat
- I would used the option
FixedFlowRate for the field of Zone Minimum Air Flow Input Method and add the max and min flow rate in the respective fields;
Fan:VariableVolume
- Use the option of FixedFlowRate for the field Fan Power Minimum FLow Rate Input Method
and add the max and min flowrates;
Controller:OutdoorAir
- verify the OA flowrates are modelled accurately;
AirLoopHVAC
- can be autosized.
As per the I/O ref guide, Sizing:System
is used for calculating system sizing for every design day in the IDF and the max heating & cooling air flow rates and capacities are saved for use in the component sizing calculations.
Once Did you run a model with HVACTemplate objects, it is a good idea to verify that the inputs field System Availability Schedule Name
, Supply Fan Maximum Flow Rate
and Supply Fan Minimum Flow Rate
for all objects in the expidf to make sure that the inputs in the HVACTemplate objects get translated as desired.
group DesignSpecification:OutdoorAirHVACTemplate:System:VAV - just to make sure that the OA flowrates are modelled accurately;
- I correctly? You would used the option
FixedFlowRate for the field of Zone Minimum Air Flow Input Method and add need to hardsize the max and min flow rate flowrates in these objects and apply the respective fields;appropriate schedule in this object.
Fan:VariableVolume
AirLoopHVAC
- can be autosized.
Hi @Anna
Did you verify that the field System Availability Schedule Name
for all objects in the group HVACTemplate:System:VAV
are modelled correctly? You would need to hardsize the max and min flowrates in these objects and apply the appropriate schedule in this object.
Hope that helps,
Raghu