There are many control logics one could implement for this specific purpose, the "best" theoretical one being a combination of differential enthalpy and differential dry bulb: you put an "enthalpy" sensor (really it's a temperature sensor and a humidity sensor, with a logic board to calculate enthalpy based off temp and humidity) in the return air inlet to ERV and one on the outdoor air inlet, and decide whether it's more appropriate to use the wheel or not.
I'm specifically mentioning "theoretical" here because the problem with humidity sensors (therefore with enthalpy) is that they can quickly fall off calibration and make the computation of enthalpy completely inaccurate. As I think I recall reading, you should likely replace them every year or so...
This ASHRAE article Economizer High Limit Controls and Why Enthalpy Economizers Don’t Work should prove a most interesting read, even though it doesn't address ERVs specifically but rather economizers. Couple of quotes:
Humidity sensors, on the other hand, are notorious for being difficult to maintain in calibration
The best option, assuming no sensor error, is the combination of differential enthalpy and fixed dry bulb
Including sensor error, the worst (or very close to the worst) option in all climates is the differential enthalpy control. This control logic is considered the “best” anecdotally among many design engineers and is required for some climate zones by Standard 189.1. Yet, in practice, with realistic (even optimistic) sensor error, it performs among the worst of all options
In EnergyPlus, relevant fields are:
- HeatExchanger:AirToAir:SensibleAndLatent::Economizer Lockout
- Controller:OutdoorAir::Economizer Control Type and the following fields
Economizer Control Action TypeandHeat Recovery Bypass Control Type
fieldsfieldEconomizer Control Action TypeandHeat Recovery Bypass Control Type
This ASHRAE article Economizer High Limit Controls and Why Enthalpy Economizers Don’t Workarticle should prove a most interesting read, even though it doesn't address ERVs specifically but rather economizers. read. Couple of quotes:
