How you define infiltration is your choice. You might want to do it only for perimeter (=exposed to the outdoor) zones, or to put a constant air change in the entire building for example. There are good reasons to choose one or another.
There are several choices in ZoneInfiltration:DesignFlowrate's Calculation Method for example (I'm linking to this object since it's the most commonly used, but there are a few other infiltration objects).
If you use Flow/ExteriorArea
or Flow/ExteriorWallArea
, any core/central zones that don't have exterior surfaces will get a resulting infiltration of zero. If you use any of the other methods (Flow/Zone
, Flow/Area
, AirChanges/Hour
) it won't care whether it's a core or a perimeter zone.
EDIT:
Here's an example to set the Flow/Zone
to 500 CFM / 0.246 m3/s, with a constant value (not depedent on temperature or wind), where Core Zones
is a ZoneList listing all the zones to apply it to, but you could also just use the name of one Zone
ZoneInfiltration:DesignFlowRate,
Core Infiltration, !- Name
Core Zones, !- Zone or ZoneList Name
Always On Sch, !- Schedule Name
Flow/Zone, !- Design Flow Rate Calculation Method
0.246, !- Design Flow Rate {m3/s}
, !- Flow per Zone Floor Area {m3/s/m2}
, !- Flow per Exterior Surface Area {m3/s/m2}
, !- Air Changes per Hour
1, !- Constant Term Coefficient
0, !- Temperature Term Coefficient
0, !- Velocity Term Coefficient
0; !- Velocity Squared Term Coefficient
, Flow/Area
, AirChanges/Hour
EDIT: