I don't think "Unit Type" is at fault here for Number of People Schedule, as long as you use either empty, dimensionless, availability or controlmode, you're fine.
Since this can be confusing to track down for anyone who's first digging in the source code, these kind of rules are defined in ScheduleTypeRegistry.cpp. Here's an extract circa L273:
// className, scheduleDisplayName, scheduleRelationshipName, isContinuous, unitType, lowerLimitValue, upperLimitValue;
{"People","Number of People","numberofPeopleSchedule",true,"",0.0,1.0},
{"People","Activity Level","activityLevelSchedule",true,"ActivityLevel",0.0,OptionalDouble()},
{"People","Work Efficiency","workEfficiencySchedule",true,"",0.0,1.0},
{"People","Clothing Insulation","clothingInsulationSchedule",true,"ClothingInsulation",0.0,OptionalDouble()},
So here, you might get that you need a number of people schedule that is Continuous, no Unit Type, and between 0 and 1. Not that simple!
Then it gets a bit trickier, and I'll give you the semi-short story. ScheduleTypeRegistry > isCompatible will:
- Ignore the Numeric Type (
DiscreteorContinuous) - Check the unit type which in turns calls ScheduleTypeLimits::units, esp L310, which is where you'll see that here really since the
ScheduleTypeRegistryis expectingemptyfor unit type, you could useDimensionless,availabilityorcontrolmodeas well. If you use say "Temperature", it won't work. - Check the lower and upper limit values, that must be included in the
[0;1]interval ([0.3;0.7]will work). They MUST be set!
Here's some code to play with and to demonstrate what I'm saying:
# Initialize an empty model with a people object
model = OpenStudio::Model::Model.new
people_def = OpenStudio::Model::PeopleDefinition.new(model)
people = OpenStudio::Model::People.new(people_def)
# Create a sch type limits
sch_limit = OpenStudio::Model::ScheduleTypeLimits.new(model)
# THE LIMITS MUST BE SET.
# Above 0.0 included
sch_limit.setLowerLimitValue(0.3)
# Less than 1.0 included
sch_limit.setUpperLimitValue(0.9)
# Whether you include the following two statements or not, it doesn't care
# If you put "Temperature", it'll fail
sch_limit.setUnitType("Dimensionless")
# It should be Continuous but it is ignored...
sch_limit.setNumericType("Discrete")
# Create a schedule and set the schedule type limit
sch = OpenStudio::Model::ScheduleRuleset.new(model)
sch.setScheduleTypeLimits(sch_limit)
# Assign the schedule, and check what the result is:
people.setNumberofPeopleSchedule(sch)
=> true
Since this can be confusing to track down for anyone who's first digging in the source code, these this kind of rules are defined in ScheduleTypeRegistry.cpp. Here's an extract circa L273:
=> true