Here are some things to explore...
- For the 5 OA (outdoor air) ACH, set your
DesignSpecification:OutdoorAir
object to 5 ACH. Make sure your ceiling height is properly defined in yourThermalZone
. Set 'Control For Outdoor Air' to 'YES' in yourAirTerminal:SingleDuct:VAV:Reheat
. - For the 10 Total ACH, in your
set your 'Zone Minimum Air Flow Input Method' to 'Fixed Flow Rate' and then convert your 10 ACH to CFM and enter in 'Fixed Minimum Air Flow Rate' field. Additionally, in theSizing:Zone
object, set the 'Cooling Design Air Flow Method' to 'DesignDayWithLimit' and then specify the 10 ACH (converted to CFM) in the 'Cooling Minimum Air Flow' field.
set your 'Zone Minimum Air Flow Input Method' to 'Fixed Flow Rate' and then convert your 10 ACH to CFM and enter in 'Fixed Minimum Air Flow Rate' field. Additionally,inthe theSizing:Zone
object, set the 'Cooling Design Air Flow Method' to 'DesignDayWithLimit' and then specify the 10 ACH (converted to CFM) in the 'Cooling Minimum Air Flow'field.field.