Hi Eric. No, the model did not have WindowMaterial:SimpleGlazingSystem in it. I changed the window to this, and it solved the problem - at least got further in the simulation process. Unfortunately, I now got 12 new errors:
- Process exited with a non-zero exit code of: 1
- Error report file indicates that the process did not complete successfully
- IP: IDF line~10241 Error detected in Object=DAYLIGHTING:CONTROLS, name=THERMAL ZONE 1 Field [Zone Name] is required but was blank
- IP: IDF line~10253 Error detected in Object=DAYLIGHTING:CONTROLS, name=THERMAL ZONE 1 Field [Daylighting Reference Point 1 Name] is required but was blank
- Out of range value Numeric Field#3 (Number of Stepped Control Steps), value=0.10000, range={>=1}, in DAYLIGHTING:CONTROLS=THERMAL ZONE 1
- Out of range value Numeric Field#5 (Glare Calculation Azimuth Angle of View Direction Clockwise from Zone y-Axis), value=1000000.00000, range={>=0 and
- Out of range value Numeric Field#6 (Maximum Allowable Discomfort Glare Index), value=0.00000, range={>=1}, in DAYLIGHTING:CONTROLS=THERMAL ZONE 1
- Out of range value Numeric Field#8 (Fraction of Zone Controlled by Reference Point 1), value=22.00000, range={>=0.0 and
- IP: Out of "range" values found in input
- IP: Blank "required" fields found in input
- IP: Out of "range" values and/or blank required fields found in input
- IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
The eplusout.err file shows:
Program Version,EnergyPlus, Version 8.6.0-198c6a3cff, YMD=2017.01.11 09:40,IDD_Version 8.6.0
************* IDF Context for following error/warning message:
************* Note -- lines truncated at 300 characters, if necessary...
************* 10509 Daylighting:Controls,
************* indicated Name=Thermal Zone 1
************* Only last 2 lines before error line shown.....
************* 10510 Thermal Zone 1, !- Name
************* 10511 , !- Zone Name
** Severe ** IP: IDF line~10511 Error detected in Object=DAYLIGHTING:CONTROLS, name=THERMAL ZONE 1
** ~~~ ** Field [Zone Name] is required but was blank
************* Only last 10 lines before error line shown.....
************* 10514 0.8, !- Lighting Control Type
************* 10515 0.1, !- Minimum Input Power Fraction for Continuous or ContinuousOff Dimming Control
************* 10516 0.1, !- Minimum Light Output Fraction for Continuous or ContinuousOff Dimming Control
************* 10517 0.1, !- Number of Stepped Control Steps
************* 10518 1, !- Probability Lighting will be Reset When Needed in Manual Stepped Control
************* 10519 , !- Glare Calculation Daylighting Reference Point Name
************* 10520 1000000, !- Glare Calculation Azimuth Angle of View Direction Clockwise from Zone y-Axis {deg}
************* 10521 0, !- Maximum Allowable Discomfort Glare Index
************* 10522 1, !- DElight Gridding Resolution {m2}
************* 10523 , !- Daylighting Reference Point Name 1
** Severe ** IP: IDF line~10523 Error detected in Object=DAYLIGHTING:CONTROLS, name=THERMAL ZONE 1
** ~~~ ** Field [Daylighting Reference Point 1 Name] is required but was blank
** Severe ** Out of range value Numeric Field#3 (Number of Stepped Control Steps), value=0.10000, range={>=1}, in DAYLIGHTING:CONTROLS=THERMAL ZONE 1
** Severe ** Out of range value Numeric Field#5 (Glare Calculation Azimuth Angle of View Direction Clockwise from Zone y-Axis), value=1000000.00000, range={>=0 and <=360}, in DAYLIGHTING:CONTROLS=THERMAL ZONE 1
** Severe ** Out of range value Numeric Field#6 (Maximum Allowable Discomfort Glare Index), value=0.00000, range={>=1}, in DAYLIGHTING:CONTROLS=THERMAL ZONE 1
** Severe ** Out of range value Numeric Field#8 (Fraction of Zone Controlled by Reference Point 1), value=22.00000, range={>=0.0 and <=1.0}, in DAYLIGHTING:CONTROLS=THERMAL ZONE 1
** Severe ** IP: Out of "range" values found in input
** Severe ** IP: Blank "required" fields found in input
** Severe ** IP: Out of "range" values and/or blank required fields found in input
** Fatal ** IP: Errors occurred on processing IDF file. Preceding condition(s) cause termination.
...Summary of Errors that led to program termination:
..... Reference severe error count=9
..... Last severe error=IP: Out of "range" values and/or blank required fields found in input
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 9 Severe Errors; Elapsed Time=00hr 00min 0.39sec
Apparently there are some problems with the daylight control and the thermal zone name? Any ideas? :)
Hi Eric. No, the model did not have WindowMaterial:SimpleGlazingSystem in it. I changed the window to this, and it Thanks Eric, that solved the problem - at least got further in the simulation process.
error. Unfortunately, I now got 12 new errors:
Thanks Eric, that solved the error. Unfortunately, I now got 12 new errors:
control...
Any ideas? :)
Apparently there are some problems with the daylight control...
Any ideas? :)control...
