If this question is related to the linked one than you need first to set the heating setpoint to 26C and an EMS control logic will be similar to the code desribred here
This is the code which should work in your case
Schedule:Constant,Cycle,OnOff,1; ! New schedule object
AvailabilityManager:Scheduled, ! Updated Availability Manager
  Packaged Rooftop Air Conditioner Availability Manager,
  Cycle;
  AptTemp,
  BLOCK1:ZONE1,
  Zone Mean Air Temperature;
! Don't forget to set heating setpoint to 26C
  hSP,
  BLOCK1:ZONE1,
  Zone Thermostat Heating Setpoint Temperature;
EnergyManagementSystem:Actuator,
  AvailSCH_Overwrite,
  Cycle,
  Schedule:Constant,
  Schedule Value;
  Supervision,
  BeginTimestepBeforePredictor,
  HVAC_uncontolledloop_Supervision;
  HVAC_uncontolledloop_Supervision,
  SET Toffset = 4,
  IF AptTemp > (hSP - 0.01), ! -0.01 due to system can maintain the zone temperature very close to the setpoint
  SET AvailSCH_Overwrite = 0,
  ELSEIF AvailSCH_Overwrite == 0 && AptTemp >= (hSP - Toffset),
  ELSE,
  SET AvailSCH_Overwrite = 1,
  ENDIF;