Here's what I'd do: (link to the test model)
Create an AirLoopHVAC to serve the Data Center Zone with:
- Coil:Cooling:Water
- AirLoopHVACUnitarySystem (with WaterToAir HeatPump)
- SetpointManager:SingleZoneReheat
- AirTerminal:SingleDuct:Uncontrolled
Create a PlantLoop to act as the heat rejection loop with:
- Sizing:Plant (click dotted line in middle of loop and scroll down)
- Loop Type = Condenser
- Pump:VariableSpeed or Pump:ConstantSpeed
- Control Type = Intermittent
- FluidCooler:SingleSpeed or FluidCooler:TwoSpeed
- SetpointManager:FollowOutdoorAirTemperature
- Reference Temperature Type = OutdoorAirDryBulb
- HeatExchanger:FluidToFluid
- Control Type = CoolingSetpointOnOff
- Heat Transfer Metering End Use Type = FreeCooling
- Connect the Heat Pump Heating and Cooling Coils from the AirLoopHVACUnitarySystem to this loop
Create a PlantLoop to act as the free cooling loop with:
- Loop Type = Cooling
- Design Loop Exit Temperature = 60F
- Connect the HeatExchanger:FluidToFluid (from My Model)
- SetpointManager:Scheduled
- Make a 60F schedule and assign it here
- Connect the Coil:Cooling:Water (from My Model)
Here is the cooling rate before adding the chilled water coil and free cooling loop:
Here is the cooling rate after. Notice that the chilled water coil (blue) is picking up part of the load, and the heat pump coil (orange) is picking up the rest of the load.
EDIT Yes, the water-to-air HP is actually doing less cooling in the second picture, it's just hard to see since the scales and screenshots aren't identical. Here's a before (green) and after (pink) of the HP coils plotted on the same plot.