Don't you have a mechanical engineer on the project responsible to size the data center cooling system?
But yes, you shouldn't have any latent load, so for your coil Total kW = Sensible kW.
Without seeing your idf file (maybe you should share it), I would definitely look at how you defined your internal loads from the server. You probably used an "ElectricEquipment" object, make sure your fraction latent is set to zero there.
ElectricEquipment,
  • Name
  • Zone or ZoneList Name
  • Schedule Name
  • Design Level Calculation Method
  • Design Level {W}
  • Watts per Zone Floor Area {W/m2}
  • Watts per Person {W/person}
  • Fraction Latent: set to 0
  • Fraction Radiant
  • Fraction Lost
  • End-Use Subcategory
ElectricEquipment,
  • Name
  • ElectricEquipment, , !- Name , !- Zone or ZoneList Name
  • Name , !- Schedule Name
  • Name , !- Design Level Calculation Method
  • Method , !- Design Level {W}
  • {W} , !- Watts per Zone Floor Area {W/m2}
  • {W/m2} , !- Watts per Person {W/person}
  • {W/person} 0, !- Fraction Latent: set to 0Latent
  • 1, !- Fraction Radiant
  • Radiant 0, !- Fraction Lost
  • Lost ; !- End-Use Subcategory
ElectricEquipment, , !- Name , !- Zone or ZoneList Name , !- Schedule Name , !- Design Level Calculation Method , !- Design Level {W} , !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} 0, !- Fraction Latent Latent 1, !- Fraction Radiant 0, !- Fraction Lost ; !- End-Use Subcategory