Hi Waseem,
I replied to your question on E+ yahoo group. Just in case you haven't seen it, I am adding my answer here as well.
I was recently involved in a study between De Montfort University, Salford University and ENSIMS which faced the same issue; how to calculate number of overheating hours (in addition to other overheating criteria outputs such as CEN15251) during occupied period from. I needed a code which can be applied to a large number of simulations and I decided to try to do it in EMS. You can see the piece of code which worked for me.
Regards,
Ivan Korolija
IESD, De Montfort University, Leicester, UK
! EMS code to calculate overheating hours
! EP Macro command to set threshold temperature (you can place it at the top of the imf file)
##set1 OHTempBed 25
! Get the operative temperature from the E+ output variables (This can be dry-bulb temperature too))
    BedOpTemp,      !- Name
    Bedroom,                !- Output:Variable or Output:Meter Index Key Name
    Zone Operative Temperature;  !- Output:Variable or Output:Meter Name
! Get the occupancy schedule value to use as a reference when the room is occupied
    BedOcc, !- Name
    Occupancy_Bedroom Sch,           !- Output:Variable or Output:Meter Index Key Name
    Schedule Value;  !- Output:Variable or Output:Meter Name
! EMS programm
    Overheating,  !- Name
    EndOfZoneTimestepBeforeZoneReporting,  !- EnergyPlus Model Calling Point
    OverheatingProg;     !- Program Name 1
! If zone is occupied and temperature is above threshold, count for overheating hours
    OverheatingProg,     !- Name
    IF BedOcc > 0 && BedOpTemp > OHTempBed[],
    SET BedOH = ZoneTimeStep, ! ZoneTimeStep is built in variable which is fraction of hour specified elswhere in the model (default value is 4 which is equal to 0.25 overheating hours)
    ELSE,
    SET BedOH = 0,
    ENDIF;
  EnergyManagementSystem:GlobalVariable,
    BedOH;
  EnergyManagementSystem:OutputVariable,
    Bedroom Zones Overheating While Occupied,  !- Name
    BedOH,         !- EMS Variable Name
    Summed,                  !- Type of Data in Variable
    ZoneTimestep;            !- Update Frequency
  Output:Variable,*,Bedroom Zones Overheating While Occupied,Annual;
  • Since I wasn't able to post the following code in the comment due to length limit, I edited this answer.
It should be possible to calculate PPD over 10% by using EMS. The code (which has to be validated :) )for PPD should be:
##set1 PPDBedThershold 10
    ActualBedPPD,      !- Name
    Zone Thermal Comfort Fanger Model PPD;  !- Output:Variable or Output:Meter Name
! If you already defined occupancy sensor for the overheating hours, you should delete this one
    BedOcc, !- Name
    PPD,  !- Name
    PPDProg;     !- Program Name 1
    PPDProg,     !- Name
    IF BedOcc > 0 && ActualBedPPD > PPDBedThershold[],
    SET BedPPD = ZoneTimeStep,
    ELSE,
    SET BedPPD = 0,
    ENDIF;
    BedPPD;
    Bedroom Zones PPD Over 10 While Occupied,  !- Name
    BedPPD,         !- EMS Variable Name
  Output:Variable,*,Bedroom Zones PPD Over 10 While Occupied,Annual;
Hi Waseem,
Regards,
Ivan Korolija
##set1 OHTempBed 25
    BedOpTemp,      !- Name
    BedOcc, !- Name
! EMS programm
    ELSE,
    SET BedOH = 0,
    ENDIF;
    BedOH;
    BedOcc, !- Name
    PPD,  !- Name
    PPDProg,     !- Name
    ELSE,
    SET BedPPD = 0,
    ENDIF;
    BedPPD;