The culprit in this case turned out to be bad u-values for the walls doors of the walk-in coolers in this supermarket model. This resulted in a very large heat removal from the adjacent zones causing a very cold air temperature to be passed to the psychrometric function which tripped the fatal error.
How did we find this?
- The full error message included "tdb=[-427.76]" which gives a clue that something is very cold.
- The autosized heating supply air flow rate for some zones was very high (e.g. 1107880 m3/s). This gives a clue that this is an envelope or internal gains problem, because the full system is not modeled during sizing.
- The refrigerated cases and walkin coolers were the likely cause of the large heating load. Tested this by deleting all refrigeration objects, and the error was gone.
- After poring over the details of all the refrigerated cases, @apetersen found the problem in the walkin coolers. Every one of them had these inputs:
Refrigeration:Walkin,
255.599352755867, !- Insulated Surface U-Value Facing Zone 1 {W/m2-K}
255.599352755867, !- Glass Reach In Door U Value Facing Zone 1 {W/m2-K}
255.599352755867, !- Stocking Door U Value Facing Zone 1 {W/m2-K}
The culprit in this case turned out to be bad u-values for the walls doors of the walk-in coolers in this supermarket model. This resulted in a very large heat removal from the adjacent zones zone causing a very cold air temperature to be passed to the psychrometric function which tripped the fatal error.
The culprit in this case turned out to be a bad u-values for the walls doors of the walk-in coolers in this supermarket model. This resulted in a very large heat removal from the adjacent zone causing a very cold air temperature to be passed to the psychrometric function which tripped the fatal error.